Once the outer sheath is removed from the SWA it needs to be enclosed in conduit, the bedding layer is not compliant as an outer sheath and cannot be left unenclosed.To get rid of the outer sheath I was going to use an adaptable box with a SWA gland one side and a stuffing gland holding the inner circular section in the other side, before finally going to the individual cores for that drop.
That does not comply for protecting a cable buried in the wall, with the armour removed, and conductors protected by PVC conduit, it will have to be protected by 30mA RCD.The cable will indeed be RCD protected by a 100ma RCD protecting the cable itself and then 30ma RCDs in the outbuilding.
The intention was either to terminate in there or second choice would be a normal torpedo joint and going down the cavity therefore remaining 100% SWA.