Discuss Differences between OSG and Big regs book in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
DanBrown
Has anyone noticed any differences between the New ON-SITE GUIDE and the Big Red 17th Edition regs book?.
I have noticed that some max permitted zs values are different.
For example
OSG says BS EN 60898 TYPE B 32A = 1.16 ohms
and
Main 17th Regs book says BS EN 60898 TYPE B 32A = 1.44 ohms
Is it just me reading it wrong?
if im correct, which one are you supposed to be following? as their both current 2008 17th.
Thanks in advance...
For example
and
i think you will find that 1.44 bs7671 (big book ) is the max Zs while the OSG 1.15 is the corrected value for temp (80% );)
That is it, the RULE OF THUMB! been around for years under 16th it was 75%, now under 17th it is 80%. it is all about making an allowance for the cable warming up and therefore its resistance increasing as current flows in the cable. clever stuff ehh!
it was like this with the 16th regs and OSG as well.
So why have they temp corrected in the OSG but not in the regs then?......:rolleyes:
Well for those of you that wish to know...(and I must presume you do), the values given in the tables are given PRESUMING that you are also going to be using Table 7.1 rather than carrying out conventional design (as you would tend to with the full regs)
So basically, you calculate your Ib, size your In (protective device) accordingly, look it up in table 7.1, pick your installation method and earthing arangements, and you will get the max cable length for your cable size - and funny old thing, if you stick to that, then your max Zs will comply with the values given in the table (if your Ze is 0.35/0.8 as appropriate), and of course if its lower, then so will be your Zs.
(apologies to anyone now egg sucking, but some of the guys are starting in college):)
Reply to Differences between OSG and Big regs book in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
I have been going round in circles with this question. I just cant seem to get an answer remotely close to the options. Continuity of a ring...
Hi, as an aspiring sparky I'm needing help with the temperature adjustment formula for Zs. I'm using GN3 (17th). I understand that the values...
Hi Guys, I'm doing my Level 3 C&G design project and just have a few design related queries which i am so far struggling to find clarity on...