Hello,
I need to add a switch for an outside light. The obvious place is near the back door but that is where the fire call point will go.

Is there a minimum distance in any regualtions between the two?

E.g. to prevent someone from accidentally pressing the call point while trying to press the light switch.
 
call points are generally mounted @ 1200mm. this is also the recommended height for your switch, under part M. sod part M. safety circuits take precedence. stick the switch higher up.
 
As long as the switch does not distract from the call point it shouldn't be a problem. If the switch is going to be surface mounted then it may well do if the call point is not conspicuous from all directions in particular the main route of travel past it.
 
I'll look it up but thought CP'S were 1400 but was a flexible rule if you want to match existing switch heights, if you consider accidental operations the a lift up cover will usually suffice as mentioned.
 
The fact its red just isn't enough for some people.
agree. the numptys need a red flame symbol stuck on the wall to indicate that it's not a light switch. then they'll think it's a fire extinguisher.
 
MCPs are 1400mm +/- 300mm. so my 1200 falls within.

Light switches are 450mm-1200mm. what idiot wouldfitalight switch @450mm?
 

Reply to Distance fire call point to light switch in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
3K
This is in regards to wireless light switches i posted to two other forums. Surely someone here has some experience with the switches that is...
Replies
4
Views
1K
This weekend I was replacing a hall light fixture in my old home (rewired circa 1980/90's) and noticed the work was done using one of the exposed...
Replies
1
Views
1K
Hi, I have ran a light ring off a fused spur with two lights on, each with their own switch (outside and lobby light) I want to put the outside...
Replies
4
Views
2K
I bouught a Nissan Townstar EV and have found what I consider a theft problem All previous vans I have had allowed the driver to enter and exit...
Replies
3
Views
619

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock