well then providing the zs readings at the caravan sockets comply with the regs and section 7 details, not sure of what actual reg it is without looking there is no issue, seems fine to me, if you have the cable sizes worked out and rcd protection at the sockets and tt arrangments with zs readings within parameters then all fine IMO, I would prefer local earth rods myself, but hey if theres a rod and the readings are right I can't see a problem unless I'm missing something.