been reading that all stranded cable terminations have to be crimped and that this is a reg, not sure as i cant find it. Is this just for fine stranded flex or does it apply to any cable that is stranded ?

at present when using single stranded cable i twist the strands of the single cable and terminate to switch/socket/light or MCB, should i be fitting bootlace crimps instead ?
 
if it's 7 strand cable, no need for ferrules. it's when you've got the multi stranded fine strand cable that you need to think of ferrules/crimps.
 
It's always a better connection with a crimp termination but there is no regulation other than the usual 'mechanically and electrically sound' proviso.
 
if it's 7 strand cable, no need for ferrules. it's when you've got the multi stranded fine strand cable that you need to think of ferrules/crimps.
This was exactly my thoughts, the finer stranded panel wiring is prone to damage when terminated with the wire directly under a screw but normal house wire is fine without bootlace ferrules.
 
I certainly don't do it on light pendants (unless the manuf has already done it). The only other place I use stranded is singles and I've not currently done there either (which may be poor practice and I should possibly change to doing so?).
 
Please open the Technical data sheets on Marvo's link to RS there is a French colour code and German colour code for bootlace ferrule sizes which are different.
 
Last edited by a moderator:
526.81 In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
Apart from using suitable terminals, this can be achieved by doubling over the conductor or using a boot lace ferrule/crimp.
 
I have to say I don't like using crimps unless I have to. The way I've been taught is to consolidate the ends of cable (twist them to a degree to make it as though solid but not so much to reduce the csa). You have to bear in mind when using a crimp you have placed your trust in two thing (with two things to go wrong: the crimp and the screw). I'd much rather without the use of a crimps but it seems I am swimming against the waves on this one as the crimps does add a sense of tidiness to a connection and more and more sparks have taken them on board of recent. Just thought I'd my view on them thanks.
 
In a clamp type connections bootlace ferules reduce the contact area due to the conductor not being allowed splay out. I’ve experienced problems in control panels where multiple bootlaces have been used in one clamp terminal where one has clamped tight the other has vibrated out.

I don’t like them. They have caused me hours of unnecessary fault finding commissioning new plant.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Do all stranded cables now have to be crimped ??
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
ianphilip007,
Last reply from
Marvo,
Replies
17
Views
24,575

Advert

Back
Top