As opposed to arguing the right and wrongs, what is your background.
I worked in electronics and programming for over 40 yrs before semi retirement and now work to suit mostly repairing various radio test equipment from all over the world, for 3 days a week i look after 21 cottages on a holiday complex mostly electrical.

Things like this but now more as a hobby
 

Attachments

  • 2018_07_24_10_38_B7ECA58B-EEFF-436C-8FC8-F636668A93C2.JPG
    455.6 KB · Views: 42
  • 2020_11_25_17_38_IMG_0648.JPG
    711.5 KB · Views: 41
Last edited:
I worked in electronics and programming for over 40 yrs before semi retirement and now work to suit mostly repairing various radio test equipment from all over the world, for 3 days a week i look after 21 cottages on a holiday complex mostly electrical.

Things like this but now more as a hobby
Love the workshop.
I still stand by everything I have said though.
if you don’t have the info you can’t make the call for correct advice.
 
You have no idea what the project is

That is correct mate. All we know is it's a place where someone has decided they want a way to isolate the power for trainees.
Why do they want this? What are the dangers that they have requested this? What level of injury could happen?
The project may just need a key switch that can isolate the power, or it may need a push button that is monitored and wired to a safety device. Only a risk assessment will answer this.
 
You are being ridiculous, you have no idea what he's switching it, maybe a spa pump for instance.

He simply asked if they did a 20 amp stop switch, and you accused me of missing the point, when in fact it was you who missed the actual question.
With all respect to the conversation, your premise of ridiculous is not founded by any of the posts, we simply do not have the info to make such accusations, if this is for course work then we don't permit direct answers only nudging but is this is real then we indeed need to question the context of his circumstances because this falls in a category that information is crucial to responses.
 
a point that has been missed so far, unless i've missed it, is that a stop button is wired into the control circuit, so no way will it ever see a 20A load current.
 
a point that has been missed so far, unless i've missed it, is that a stop button is wired into the control circuit, so no way will it ever see a 20A load current.

I think the OP's intensions were to use the stop button as an isolator and wire directly into the power circuit.
 
a point that has been missed so far, unless i've missed it, is that a stop button is wired into the control circuit, so no way will it ever see a 20A load current.
This is why the op was asked what the stop button was for and advised that its not as simple as just wiring in a "stop button". would have been just easier to search on google for the 20amp switch, than ask on this forum, if there is no intent on taking advice or explaining what the job is.
 
This is why the op was asked what the stop button was for and advised that its not as simple as just wiring in a "stop button". would have been just easier to search on google for the 20amp switch, than ask on this forum, if there is no intent on taking advice or explaining what the job is.

That's what the op did, he said he basically just wanted to know if a 20 amp stop switch existed, as he couldn't find one.

I get the questions being asked concerning a risk assessment, but the op a number of times said that he just wanted to know if one existed and wasn't interested in anything else.

I'm sure if he is learning in a training environment, then the trainer will put him right.

If the op returns, then maybe he can explain the scenario.
 
That's what the op did, he said he basically just wanted to know if a 20 amp stop switch existed, as he couldn't find one.

I get the questions being asked concerning a risk assessment, but the op a number of times said that he just wanted to know if one existed and wasn't interested in anything else.

I'm sure if he is learning in a training environment, then the trainer will put him right.

If the op returns, then maybe he can explain the scenario.
Yeah, but is an unusual request so quite rightly raised interest in what it was required for.
 
That's what the op did, he said he basically just wanted to know if a 20 amp stop switch existed, as he couldn't find one.

We understand this. But there is more to it than that.

Lets say we go with his first post.... We give him a stop button that can do 20A...
He then sticks it in his circuit and then someone comes along and says "According to table 537.4 you cant use that stop button as an isolator". He replies "But I was told I could... on a forum"

Things are rarely straight forward in our work.


I get the questions being asked concerning a risk assessment, but the op a number of times said that he just wanted to know if one existed and wasn't interested in anything else.

Again, see above.
 
I worked in electronics and programming for over 40 yrs before semi retirement and now work to suit mostly repairing various radio test equipment from all over the world, for 3 days a week i look after 21 cottages on a holiday complex mostly electrical.

Things like this but now more as a hobby
Dear mainline,

I gather Gibsons jigsaw company are looking for a suitable picture to continue their ‘workshop‘ category of puzzles. 🙂

Thank you for the great photos of your lab bench. It clearly is a place where work is indeed done.

Regards

Marconi

1657724965204.png
 

Attachments

  • 1657724789337.png
    525.9 KB · Views: 35
Dear mainline,

I gather Gibsons jigsaw company are looking for a suitable picture to continue their ‘workshop‘ category of puzzles. 🙂

Thank you for the great photos of your lab bench. It clearly is a place where work is indeed done.

Regards

Marconi

View attachment 99430
Thanks for the kind words

A place where work used to happen.
 

Attachments

  • shack.jpg
    63.5 KB · Views: 27
Last edited:
Fair point, however I have never seen a training environment where the "training is wire up this spar pump"

like I said, if the risk assessment deems it suitable then go ahead but i think it is a vital step that both you and the op are missing.
OP, has anybody done a risk assessment and if so, what stop category are you trying to design. also, is a single point of failure likely to bring a risk of significant harm to anybody?

I am done with this for tonight and my final thoughts are Simpley that on the face of it neither @mainline or @j_arney have the information and knowledge required to design a suitable safety system for this project.
 
Hey
Im back and done the job. In the end I had a 6amp circuit feeding the stop button then the coil and 20 amp circuit supplying a socket via a rotary isolator and contactor.
So you had a stop button and rotary isolator switching the socket on and off. I was asked to do this for a colleague at one of our sites and have no idea what he intends to do with this system. He’s designed it, he’s an engineer and I haven’t asked any questions. I can totally understand the repercussions from making mistakes in certain working environments and appreciate all the feedback. I’m on this forum to hopefully learn a bit, but sometimes there’s no need for some of the negative/ condescending replies.
 
If this is paid work and invoiced you better have a paper trail of proof to who designed it and takes responsibility otherwise it still falls at your feet, imagine is someone is injured or worse, do you expect them to put their hands up to possible dangerous installation practices or point the finger at you showing your invoice.

If you are invoicing it it would be an idea to make it part of the invoice declaring no responsibility for design or safety making it clear it was requested, this would not remove you from and possible legal action because unless you have a full paper trail to this the responsibility lies on you to assess any requests meet standards applicable, so tread carefully.
 
Hey
Im back and done the job. In the end I had a 6amp circuit feeding the stop button then the coil and 20 amp circuit supplying a socket via a rotary isolator and contactor.

This is intended as a constructive comment. Where possible I would have fused down the 20 amp circuit for the coil. Then one MCB safely isolates the lot. It sounds as though you'd have to turn off two MCB's for everything at the contactor to be safely isolated?
 
Hey
Im back and done the job. In the end I had a 6amp circuit feeding the stop button then the coil and 20 amp circuit supplying a socket via a rotary isolator and contactor.
So you had a stop button and rotary isolator switching the socket on and off. I was asked to do this for a colleague at one of our sites and have no idea what he intends to do with this system. He’s designed it, he’s an engineer and I haven’t asked any questions. I can totally understand the repercussions from making mistakes in certain working environments and appreciate all the feedback. I’m on this forum to hopefully learn a bit, but sometimes there’s no need for some of the negative/ condescending replies.
I hope you have not seen my comments as either negative or condescending.
I have tried to remain professional throughout.

I presume you have used the 3 signature form to certify it.
He is responsible for design and has signed that part.
you have signed the parts for installation and for testing.

from your comment of “I have no idea what he Intends to do with the system” I can understand that you were unable to give more information so we could advise on how best to proceed.

if you were not responsible for designing the system in the first place I wonder why you asked for advice on how to get a 20A stop button when the design clearly didn’t require one.

just be absolutely certain that the certificate passes the design responsibility back to the person who gave you the design.
 
Then one MCB safely isolates the lot. It sounds as though you'd have to turn off two MCB's for everything at the contactor to be safely isolated?

A Mcb does not provide safe isolation, especially on a TT earthing system

After all, we wouldn't want the OP thinking that It's OK to do so he could end up killing someone :(

I can see that James actually agreed with your post 😲
 
Last edited:

Reply to Does a 20amp emergency stop button exist? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
683
Hi guys, A car showroom / workshop brand we do work for has asked us to modify a few things in the workshop. One of them being to implement...
Replies
7
Views
923
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
524

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock