H
haptism
Hi hope someone can help. A friend of mine (a builder) has asked me because I used to be an electrician (im not working in the trade anymore) if a non maintained emergency light in a small shop has to have a key switch (as per regulations). I realise the benefits of having a key switch but is it necessary. Thanks
Re: Does a non-maintained emergecy need a key switch
In a word, yes. This is for monthly, quarterly and annual testing of the battery & lamp.
Can the test not be carried out by switching off the lighting breaker ? The shop only as one room and a toilet room so there would be no issues switching off the entire lighting circuit to perform a test. Is a key switch essential s this situation ?
The annual test is a minimum of 2 hours and you will be putting the shop into darkness, that is why we use key switches to isolate power to the EM so not effecting any other circuit. Also useful for maintenance/repair and replacement of the EM. Easy to install and it is just the correct thing to do imho.
That's a good point, I overlooked that !
However, I dont think there is a requirement for the key switch, it can be turned off if necessary at the CB.
Of course, that isnt the best way, but, it complies AFAIAA.
As for losing the lights when the test is being done, just do it out of hours, or in daylight hours, or provide temporary lighting via a socket outlet.
well Tazz is the man for this, but IMO it doesn't need one, that said any spark worth anything would insist on fitting one.
Not really, no. But the advantage is that the emergencies can be tested without affecting the supply to the general lighting, which obviously might be desireable. Also bear in mind particularly when doing full duration tests that the batteries will take some time to charge back up, so don't carry out the test when they might be needed.
Some emergencies are self-testing as well and DALI controlled.
A thorough read of BS 5266 is obviously the best advice.
Whenever it is specified that there is to be a key switch for each E/L, switching only that E/L it always worries me it will just be left switched off and because it doesn't affect any lighting in general use no one will notice.
If using a test facility e.g. a keyswitch then you don't want it to affect the general lighting and plunge the entire area into darkness. You are simply trying to establish that the emergency luminaires will come on on failure of the local lighting.
Agree on one hand, but on the flip side, what happens when somebody comes along and switches it off without realising the consequences/ forgets to to go back and switch it back on after a full 3 hour discharge test.
Each method of doing it has advantages and disadvantages and as far as I know neither is 'incorrect' according to regulations.
8.3.3 of BS 5266-1 states "8.3.3 Test facility
Each emergency lighting system should have suitable means for simulating failure of the normal supply for test purposes (i.e. without interruption of the normal supply)."
Emphasis mine.
Emphasis mine.
Thanks for the regulation as mentioned; however the word SHOULD is not the same as MUST, so on that basis I presume that it would raise an eyebrow not to have a key switch although the system wouldn't be condemned.
If you wish to make an excursion from the regulations then you need to show good reason and ultimately show the safety of the system or persons is not compromised, for the latter points is hasn't compromised safety so not an issue there really so if this is existing set-up then only a recommendation can be issued, if this is a newly wired/fitted E/M set-up then there should be no reason IMHO that such a simple addition is not included in the design and I would be asking the Electrician to provide a very good reason as to why regulations have not been followed.
A competent Electrician will use and follow the BS7671 to the T and not to do so without good cause is poor work ethics and bad practice. Just because the wording is should instead of must shouldn't be a point argument, the BS7671 are a guidelines for good and safe work practice and are not statute law hence the phrasing 'should' instead of must. Showing you follow such guidelines as the BS7671 is your proof of good work practice and is invaluable as evidence of competency if you are ever ask to prove it in a court of law.
doesnt half make life easier testing with a switch , as for forgetting to switch them back on thats upto the person testing the indicators are so bright these days there is no excuse for not noticing them not charging so easy to spot when not switched out of test mode