No.....mostly.
If the radiator is in a special location as defined in the BRB supplementary bonding may be required between conductive and extraneous conductive parts.
This is where the confusion comes in. An extraneous conductive part is defined as a metallic part not forming part of the electrical installation and and liable to introduce a potential,generally earth.
A radiator is not liable to introduce an earth potential and is therefore not an extraneous conductive part.
The pipes supplying the radiator however may be extraneous conductive parts and so may need supplementary bonding within a special location.
An exception may be where a radiator is fixed to structural steel within the fabric of the wall for example, and so may introduce an earth potential to the special location.
Extraneous conductive parts within a special location can be metallic services which may introduce an earth potential to the special location from outside the special location but still within the equipotential zone, and may require supplementary bonding due to the perceived increased shock risk within a special location.
Extraneous conductive parts coming from outside the equipotential zone would require main bonding whether within or not within a special location.
In the example of a radiator fixed to structural steel within the fabric of the building,this steel would likely have been main bonded elswhere if it was part of the building structure in contact with the ground,but the radiator within a special location would be an extraneous conductive part within that location and so may need to be supplementary bonded.
GN8? look at GN7 Reg701.415.2,701,411.3.3 ,411.3.1.2 ,411.3.2, 415.2.2 701,415.2