O
officer dibble
I have just had a kitchen extension plus one living room built which will require wiring. In the original house there is a wire-fused consumer unit (no rcds) and an additional one for the last extension built in the 80's(no rcd but mcbs). My builder has advised me to have a single modern consumer unit fitted to service the entire house and extensions. My problem is that the original house was built in the 1960's and does not conform to modern regulations.It has ring mains and pvc cable but in grey sheathed black and red cable and the sockets don't have earth sleeves ( I could have all the sockets replaced and this remedied though). I don't know whether it will require completely rewiring to meet modern regulations even though the wiring "seems" fine.The 80s CU could service the new extension at by extending the ring mains and lighting circuit. I need advice on whether to go for a single modern consumer unit
or
add an rcd and mcbs to the 60's CU and add a separate rcd to the 80's CU which will serve the newest extension as well and have this CU tested for IET compliance
or
upgrade as mentioned before but one rcd for both existing CUs' (which needs doing anyway for safety reasons) but have yet another CU fitted which will only service the newest extension but is certain to pass all current IET regulations.
I don't want to fall foul of modern regulations and pay for a complete house rewire as the existing circuits are still servicable and should have passed regulations at the time of installation.
I would welcome any advice.
Get an independent sparky or 2 round and see what they suggest.
Generally builders do not know enough about electrics except to baffle unsuspecting customers
Upvote 0
First thing to get a grip of here is the fact that the regulations are not retrospective and so existing installations that are still safe and serviceable are not required to adhere to the new regulations.
What an electrician will do is test your existing installation and tell you what is wrong, if anything is and advise accordingly.
So now we have established this what my advice would be. Though your system is old, it may still be in very good condition, and the electrician that will test this will prove either way. I would recommend that just for continuity it would be better to have the one single CU, rather that an hodge podge of 2 to 3.
Then the safety aspect you will have with all your circuits having the additional protection by RCDs is a plus as well
Upvote 0
Depending when in the 60's it was wired you may not have earths in the lighting circuits but all your sockets should have a earth which may or may not be sleeved green or green & yellow.
Upvote 0
With one important exception ..... if your earthing and main bonding cables are not compliant with today's regulations these will need to be upgraded as part of the 'new' work.
My recommendation is that you commission an Electrical Installation Condition Report on the existing installation. This will identify any potentially dangerous conditions in addition to any non-compliances with the current regs. This then gives you the opportunity to put in place a programme of improvements where your primary aim should be to fix potentially dangerous conditions (which will have a C1 or C2 code on the EICR) and then give consideration to the merit of complying with current regulations on a case by case basis (which will be identified as C3 or even no code on an EICR).
To achieve this you will need to engage a trust-worthy and experienced electrician, not somebody who is just interested in follow-on work. A key qualification to check for is the City & Guilds 2391-10 "Electrical Inspection and Testing" Level 3 certificate or an equivalent.
Its good to see you asking the questions that you have, you are on the right track!
Upvote 0
Thank you for pointing this out EA, but all new work has to be compliant with the new regulations be it earthing, bonding or sockets etc
If you found a lighting circuit wired in 1.00mm on an existing installation with a 32 amp protective device would you on a CU change supply that circuit with a new 32amp device, I don't think so.
The same with Earthing and bonding if it requires upgrading then you have to upgrade it, but remember that regulation 132.16 states that it "Shall be Adequate" for the protective measure applied, so often it may not be required to upgrade.
Upvote 0
Yes indeed, as you say.
Although not available as PDF download unfortunately I keep a stock of these pamphlets in my van as it helps to explain why I'm asking where the water stop-cock is when I've been called in to quote to put some new lights in!
News : Electrical Safety Council
Upvote 0
Where could obtain a pamphlet?
Upvote 0
What would I expect to pay (approx) for a periodic inspection. The house a 5 bedroom detached house with 6 wire fuses CU and a 4 rcd CU.
Upvote 0
Its a day's work, I would charge £190. Electricians round your way may charge more or less of course!
Beware if you get quoted significantly lower than this. 10 circuits in a 5 bedroomed house is a day's work for one person doing the job properly IMO. If somebody tells you it can be done in 3 or 4 hours do check what you are really getting!
Upvote 0
If an old installation such as mine has been modified say by the addition of a spur to the ring main at some point, what impact does this have on compliance
Upvote 0