L

laxmi

Hi,

How to test an earth electrode resistance for Lightning Protection System in the middle of large concrete pad? I cannot not find a soft ground for spikes to drive in for testing. Is there any other ways of measuring the earth electrode resistance value?

Thanks

Laxi
 
Last edited by a moderator:
Have a look at hiring (or purchase at £500+) an earth resistance clamp which induces a current into the system without you needing to disconnect the main earth.

Or, as above an impedance test
 
Have a look at hiring (or purchase at £500+) an earth resistance clamp which induces a current into the system without you needing to disconnect the main earth.

Or, as above an impedance test

The trouble with those earth clamps, is that you need room to get the jaws around the earth rod, and there is generally very little room to do this when earth rods are within a flush to ground earth pit...

EDIT... How many electrodes (earth rods) are there along each side of the building being tested and how far apart are they?
 
Last edited by a moderator:
The trouble with those earth clamps, is that you need room to get the jaws around the earth rod, and there is generally very little room to do this when earth rods are within a flush to ground earth pit...

EDIT... How many electrodes (earth rods) are there along each side of the building being tested and how far apart are they?

Hi,
Thanks for your help on this matter. I am actually testing earth rod resistance for Lightning Protection System. There are four down conductors on each corner of the building. I managed to measure all three earth rod resistance value. But there is no soft ground around the electrode rod that belongs to fourth down conductor. One 2 m long copper solid rod is being used on this down conductor . The nearest soft ground is approximately 40m away from the test point. The surrounding area is concrete pad.

Is there any means of testing the earth electrode resistance for Lightning Protection System?

Thanks

Laxi
 
Unless this building is very small say 10m to 15m square, then it doesn't sound like you have enough down conductors depending on what the building is and building construction material.

You could use weighted metal plates in contact with ''wet'' concrete in place of your test spikes and compare values with that of the other 3 earth rods. BTW i've more often than not used test leads in excess of a 100m for the C1 test spike. So 40m isn't, as far as i'm concerned any great distance when testing earth rods...
 
Hi,
Thanks for your help on this matter. I am actually testing earth rod resistance for Lightning Protection System. There are four down conductors on each corner of the building. I managed to measure all three earth rod resistance value. But there is no soft ground around the electrode rod that belongs to fourth down conductor. One 2 m long copper solid rod is being used on this down conductor . The nearest soft ground is approximately 40m away from the test point. The surrounding area is concrete pad.

Is there any means of testing the earth electrode resistance for Lightning Protection System?

Thanks

Laxi
if you are using Megger equipment to do your testing there is no need to sink the spikes if you can't. Speak to Megger technical and they will walk you through the test procedure.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earth Electrode Testing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
laxmi,
Last reply from
laxmi,
Replies
10
Views
3,083

Advert

Back
Top