Discuss Earth Fault Loop Impedance... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi there, I’m just hoping someone could clear something up for me at all. I’m just working my way through some test questions and I’ve come across one in which isn’t making sense to me.
Q. Calculate the maximum earth fault loop impedance permissible for a 30mA RCD used to protect a circuit connected to a TN-S supply.
A. 230/0.03 = 7666ohms (if a TT system, use 50volts, but must use 230volts for a TNS and TNCS system)
Does this all seem correct, or should the question be asking for PFC rather than impedance? If I am misunderstanding, then a short explanation would really put me on the right track with this.
Thanks again in advance for your invaluable help forum.
R=E/I wher R=1667,E=50V, I=0.03. hope this helps.
I still don't see the need for them changing it.
I can't see any need for it either, if a circuit has got to 1667ohms there's something seriously wrong, let alone 7667ohms!
Plus people seem to blissfully ignore manufacturers requirements. For example if you look at the instructions for a schneider RCBO it stipulates 100ohms maximum.
Been a while since I last used a Schneider RCBO but they also stated that they couldn't be used on TT installations.
I think with the new generation this caveat has been removed.
I think it's still the same, ive just fitted a board with the new plug in neutral type, I'll see if any of the instructions are still hanging around tomorrow.
Schneider make both single and double pole RCBOs so you need to be careful which ones you order.
Aware of this, however the original ACTI9 RCBOs wouldn't operate without a decent reference to earth through the functional fly lead. Meaning in poor TT conditions, they may never operate.
I wonder how may other RCBO's which have the earth reference connection have the same limitation?
Why?
You don’t need DP rcbo’s on a TT
A DP main switch or 4 pole will give you your isolation
If you read their instructions they state that their single pole RCBOs are not suitable for TT systems.
Wonder why that is ?.
There is no requirement to switch/disconnect the neutral during over current conditions for a TT or TN arrangement except for certain requirements in part 7
Reply to Earth Fault Loop Impedance... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Can someone explain this to me? The regs book calls Zs 'Earth Fault Loop Impedence' and the On-Site Guide calls Ze 'Earth Fault Loop Impedence'.
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Hi guys was having a conversation as a apprentice I’m still not sure and was wondering why earth fault loop impedance is important if you’ve...