All - Just thought I'd let you know that the problem is resolved. The issue was on the Consumer Unit - a 1980's Hager model. Across the bottom of the single load unit (with one ELCB remember) was a brass coloured bar to house the MCB's (all experienced electrician's reading the thread are already going - I know what's coming next ... :wink_smile: ). On this bar, but not visible when standing on the ground for a shortarse like me was a 1/8 inch gap. When I selected an MCB to use, I wired up the neutral to the neutral bar on the right, which had spaces available, but the MCB I selected was to the left of this gap in the bar which had no free spaces on the neutral bar.
Under no load this circuit was fine, but under load it tripped the ELCB. A bit of careful rewiring of the Board and everything is now fine.
So, another day's experience, another thing learned - (i.e. 'assume' nothing) and (hopefully) it'll stay in the memory bank.
A genuine Thank You to everyone who took time to reply to the OP.
KK