• Electrician Forum
    Welcome to Electrician Forum. We started out on April 22nd 2006 and used Electricians Forums as our brand name which is an unregistered trademark.
Sorry, I'm tired. ...Through all socket points tested & also using a voltage pen on the cpc teminal in the ccu
OK, are you measuring 40V between the DB earth bar and the neutral bar?
If so, then there's a high resistance somewhere in the cabling or components between those two bars and the supplier's head where they should be joined (as this is supposed to be TN-C-S).
As in the main switch, Neutral tail or main cut out connection?
Yes, if you have a significant voltage between N and E in the board when under load.
Worth checking for volt drop between incoming neutral terminal on main switch and neutral busbar.
I'd be checking tightness of terminals on main switch, link to neutral busbar, and anything else you can get at that isn't sealed up. Careful of any parts that aren't isolated, of course.
Hi,so you have a potential,between your probes,a very short distance from where those two points, are one and the same.
If you draw that scenario out,identifying the parts concerned,a clearer view of what may be occurring,will reveal itself :smug:
Reactions: 1 person
I'm sticking by my previous conclusion.
I'm thinking if the bonding was disconnected you would have 230v between the bars as I don't think you have a neutral.
Turn the main switch off and do a l-n loop test on the incoming side.
That will soon tell you.
Rather than guessing at different voltages.
Reactions: 1 person
Cheers for that handysparks. I will investigate that. The whole installation is a bit of a joke so it wouldn't surprise me if it were the case of oversheared tails or untightened terminals (although I did check all the ones on the N bar & RCDs, I didn't check at the main switch).
Cheers again for everyones input. Appreciated
If the supply neutral is lost, how would that give rise to a significant voltage between neutral and earth bars in the DB, given that they're joined at the head?
Sorry rich. just seen this. I will put it on my list to check. cheers