whats the type and rating of the overcurrent device feeding the supply to the outbuilding.....
whats the type and rating of the overcurrent device feeding the supply to the outbuilding.....
well this is what i was getting at a bit earlier in this thread eng......DNOs dodgin out of their responsibilities again.....keeps surfacing this one doesn`t it?!!....My heads sort of spinning here!!! What have you connected the SWA (earthing) of this cable too, at the origin in the house and how have you connected it?? I take it you have glanded both ends??
I really don't know why you have rodded this out building, if the DNO provided earthing point is not functioning at a suitable protection level, they are duty bound to maintain it, even if it means PME'ing the supply if it's available...
Your earth rod(s) will come in handy then, as a locally installed part of the multiple earthing arrangement!! lol!!!
yep...this is why i refered to Zdb earlier....Did we ever find out the ZE of the main premises that the SWA was connected too?
As the 1.48 ohms is at the outbuilding so its not ZE !!!