Hi I am new to the forum and looking for some advice.

I was supposed to have a vehicle to grid car charger installed last week. But they couldnt get a suitable earth from the earth rod. The earth rod reasing was 384 ohms. They're saying I need a marconite pit. the reading has to be below 100 ohms. Do i have any other options? I cannot use a matt:e box.

Would driving the rods deeper get it under 100 oms? a 8ft or 12ft rod? Or do I need a bentonite or marconite pit?

Any help appreciated.
 
Use a Zappi charger and/or get someone qualified to install one. No issue with earth rods then. The cost of the proposed works will most probably be more than the extra for a Zappi!
 
I want to use the Vehicle to grid charger instead of a zappi charger. The V2G charger needs a earth rod. They have said they don’t have someone in my area who can install the earth rod. That’s why I’m asking for advice.
 
Hi - I wouldn’t be too happy with that rod for use at my home and I’d be looking to understand 5e reading and improve it if possible. It might be a corroded connection for example (?). If you’d like some help with investigating and putting in more rods I’m sure someone here would be able to help you.
 
Is the earth rod you are talking about an existing setup for your home, or one put in specially for the charger?

As Wilko says, its not very good as the IET guidance says above 200 ohm is suspect.

It could be a badly corroded copper clad rod (not likely if solid copper/brass of course) or you have very dry soil (unlikely recently!) or something strange is happening.

If it is due to the soil type, etc, then you can go deeper or put in more than one rod suitably spaced. Neither are linear (i.e. you need roughly 2.5 times rod length for half resistance) but are easy option.

Finally if putting in a new rod, or much longer one, check for pipes or cables first!!!

Background info for the interested (or bored):

If looking for (major) utility pipes, etc:
 
Where did he try fitting it, and any idea of what sort of soil conditions are there?

Bentonite clay is often used to help earthing rods:


We had a quote a while ago for something like £13 for 25kg bag, no postage mind! Still needs a source of moisture though, it works by keeping that close to rod I think.
 
What sort of soil do you have there? (sandy/gravel/clay etc)

Did he try installing the rod close to the building foundations?

Is your driveway fully paved or is there either grass or a flower bed close by where you can dig?

Rather than a rod you could lay tape in a trench or use conductive concrete (Marconite based). Conductive concrete isn't cheap at around £100 for a 25kg bag.

EV charger installation companies tend to have quite narrow profit margins and will not want to be messing around trying to get a good reading when they could be making money installing another unit somewhere else.
 
Forget installing a rod and messing about with Marconite etc. Install one of these between the fuse board and charger. I install them on a lot of chargers in Somerset now as ground conditions or location make a rod not realistic. Simply route the supply through this box and you are good to go.
With the next generation of chargers and the current higher end models of chargers you can use PME and not have to worry about earth rods. more and more will go down this route as they update the model range.
 
Forget installing a rod and messing about with Marconite etc. Install one of these between the fuse board and charger. I install them on a lot of chargers in Somerset now as ground conditions or location make a rod not realistic. Simply route the supply through this box and you are good to go.
With the next generation of chargers and the current higher end models of chargers you can use PME and not have to worry about earth rods. more and more will go down this route as they update the model range.

Is that one of those mythical box's of tricks, JW & E5 Group talks about :)

 
Last edited:
Forget installing a rod and messing about with Marconite etc. Install one of these between the fuse board and charger. I install them on a lot of chargers in Somerset now as ground conditions or location make a rod not realistic. Simply route the supply through this box and you are good to go.
With the next generation of chargers and the current higher end models of chargers you can use PME and not have to worry about earth rods. more and more will go down this route as they update the model range.

I cannot use a Matt:e box with the V2g charger. If it was a pod point or zappi i could.
 
I cannot use a Matt:e box with the V2g charger. If it was a pod point or zappi i could.
How come? Be interested to know the reason?
[automerge]1584554274[/automerge]
Is that one of those mythical box's of tricks, JW & E5 Group talks about :)

Yes, there are some 'concerns' about them but arguably no more so than exporting PME outside the zone. The regs permit it and the manufacturers now include it in some chargers.
 
How come? Be interested to know the reason?
[automerge]1584554274[/automerge]

Yes, there are some 'concerns' about them but arguably no more so than exporting PME outside the zone. The regs permit it and the manufacturers now include it in some chargers.
Least if the rod is installed to specification, it will work as designed. Seems we are relying on manufacturers for these devices to work, with no way of knowing if they do.

Have you been sold a pup?
 
Yes, there are some 'concerns' about them but arguably no more so than exporting PME outside the zone. The regs permit it and the manufacturers now include it in some chargers.

Is that not the main concern? The exporting PME under fault conditions is dangerous for something like a car that is bound to be touched.

Looking at those boxes it appears they are designed to isolate if the voltages look wrong as whatever amendment 1 will allow (no sign of any CT), but that is not a very reliable test without access to true earth (even high Z) or similar.

It might see hearsay, but using a 3-pole RCD (or ye olde ELCB design that actually measured earth current) to check for "external" earth current as well and so isolate the car completely (L, N & E) would make a lot more sense.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Burnley
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Earthing a V2G Electric Car Charger with a earth rod
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26
Unsolved
--

Advert

Thread statistics

Created
ministrymason,
Last reply from
richy3333,
Replies
26
Views
4,619

Advert

Back
Top