i did it this way and got a different figure...

Im=√((8-0.5(25+68))²+(0.866(25-68))²


I wonder if i am typing it wrong on the calculator?

Can someone else try this method please.


Can do it like this as well

In=√((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)))

OR

x = A cos 0 + B cos 120 + C cos 240

y = A sin 0 + B sin 120 + C sin 240
N = √(x²+y²)
 
Il so going on it being 53.57A on the neutral, using the calculations in the book...

70 / 53.57 - (70/230) x (8 + 25 + 68) = -29

it says if it is greater than zero it will need an earth rod, unless I'm being thick (tell me if I am) -29 is less than zero.
 
I ended up with 70/ 53.6 - 30.3

in my rough calc I think just rounded either up or down to the nearest whole number, =>5 up, =<4 down, after all it was just a quick calc, to get a ballpark figure
 
I'm out at the moment so haven't got the BYB in front of me to look at it again, I think it's just a typo above as the calculation would not work if the brackets were not even.
 
i did it this way and got a different figure...

Im=√((8-0.5(25+68))²+(0.866(25-68))²


I wonder if i am typing it wrong on the calculator?

Can someone else try this method please.

Please see previous post ... closing bracket missing. This will result in discrepancies depending upon where the bracket is assumed to be.
 
Ok so now we have the correct figure for Im, that means we can now accurately calculate the next one that tells us the answer.

so for the purpose of moving on we shall accept that 53.57 is correct.
 
The reason I just rounded the figures up and down is because you will not be able to get an Ra smack on the calculated anyway, this calc only gives you the highest permissible figure,ideally you want to be a bit lower
 
If the extra bracket has been inserted before the sqrt then your answer is correct. Correct equation should be confirmed. When I was doing structural analysis, stress calculations, for a company making actuators primarily for the aircraft and rail sectors, MS Excel was seriously frowned upon as an analytical tool. The very good reason for this is that the method of gaining the result is hidden from the user and is not expressed in the form that it would be mathematically presented.
 

Reply to Earthing for an EV Charging Point in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Similar Threads

Hi What the Maximum number of EV charge points that you can install in a Domestic system.
Replies
2
Views
212
A question perhaps for @Gavin John Hyde or others: I have a potential customer who is looking for an EV charge point installed at his property to...
Replies
7
Views
2K
I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation. I've not done one...
Replies
37
Views
3K
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
519
Hi I currently have Megger MFT 1721, I am looking to buy the megger tester attachment for EV charging , does anyone knows if the MFT 1721 takes...
Replies
2
Views
832

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock