Well at the moment we don't have any idea as to values, construction method or any other hard data, secondly the services could change (not likely on a new build I agree), there is a formula that needs to be calculated to see what value the Ra is required to meet that particular exemption, it takes no account of existing steelwork or services that may or may not be present.
He is the man signing the paperwork to say it complies and which exemption he is using.
wrong.Ok, so...
RA ev less than or equal to 70 divided by (what is Im?)
Im -(70/230) x (8 x 25 x 8)
I being current, I don't understand what m is?
Im is the max neutral current, so having just worked it out,i think its worked out at 91A, does this figure sound like a realistic figure? I don't really know what to expect here...
Your max IM I calculated at about 53 to 54 A taking into account adding a proposed further 60A load to one of the low loaded phases assuming say L1=8A,L2 =25A, L3=68A
That is just from the information you have given, your PME rod/s in this case would need to be about 3 ohms
This is only a quick and rough calc with using assumed values
How did you come to that? can you show me the calculation how you did it please, my one came out different...?
How did you come to that? can you show me the calculation how you did it please, my one came out different...?
I cheated lol I used Tony's XL spreadsheet to calc the N current
Simon above did it long hand