The copper pipe is not an Extraneous Conductive Part & only requires earthing if cables are run within 25mm. To cover yourself, do a test. I presume that all the power circuits are protected by a 30mA RCD?
Personally, I would bond all the copper pipe in the bathroom anyway. Better to be safe than sorry.
Could you be referring to Reg 528.3.4 and the note attached to this referring to BS 6891. ?
The onsite guide section 2.3 does give guidance on this and that is where this magical 25mm distance is cited. This is a distance recommended between electrical supplies and distribution cables and gas pipes.
This though is a recommended distance for gas fitters in their BS 6891, and not really aimed at us.
I also think you mean bonding rather than earthing
)