Edit : missed the ASHP bitI fed a separate enclosure with the type B in it, surface in singles / conduit from an mcb in the CU for an ASHP.

Last edited:
Edit : missed the ASHP bitI fed a separate enclosure with the type B in it, surface in singles / conduit from an mcb in the CU for an ASHP.

The charging station shall be installed with an external RCD TypeWhat type of cable and is it buried in the wall less than 50mm deep at any point?
RCD protection is not required for fault protection in this case, it's not a domestic lighting circuit and presumably the charger isn't in a bathroom so those aren't relevant.
The requirement for RCD protection of the outlet is covered by the unit itself.
That is what the Easee functional description of the RDC-DD says.The charging station shall be installed with an external RCD Type
A in the fixed installation.
I would go along the lines of :That is what the Easee functional description of the RDC-DD says.
But it is not what the Easee charging point installation instructions say (at least the copy I read)
Part of the confusion is that Easee seem to have updated their documentation in the period Dec 24 to May25.
Including the Type A RCD in the fixed installation would surely be the way to go.
The charging station shall be installed with an external RCD Type
A in the fixed installation.
Possibly my post #13 which quotes Easee's documentation on Residual Current protection, dated Dec 2024. The discussion subsequently turned to whether an RCD would be required at all at source.Where have you got that from?
The OP has stated the charging point includes a B type RCD so any upstream RCD device must also be B type to function correctly and therefore comply.

If the charger already embodies an RDC-DD, why would a type B RCD also be required at the source of supply?
Agreed - these points were made in the admittedly rather long thread above.If the cable is buried in a wall less than 50mm deep and does not have an earthed metal protection of some sort it would be required.
Or, not applicable in the OP's case but may be for others, and RCD is required for fault protection.
Agreed - these points were made in the admittedly rather long thread above.
Having established that a (double pole) Type A RCD or RCBO seems to be needed, I just wondered why Type B was mentioned - that's all I meant!
The OP thought it had a type B RCD in it.The OP stated that the EVCP has a type B RCD in it, so we must assume that type B protection is required.
HappyHippyDad - If you haven't got fed up with this thread by now, and already turned down the job, you might be coming to the conclusion it's not perhaps as bad as you thought..Crikey, so is my only option here to take up 3 ways in the consumer unit. A type B RCCB (2 ways) fed by an MCB?
I didn't get the quote!HappyHippyDad - If you haven't got fed up with this thread by now, and already turned down the job, you might be coming to the conclusion it's not perhaps as bad as you thought..
My understanding (and this might be wrong!) is that you could use a Fusebox single module width 'miniature' double pole Type A RCBO at the CU
That's assuming you are not faced with contradictory instructions accompanying the charger!![]()
FuseBox
We have over 37 years of experience in supplying consumer units, 3 phase fuseboards and circuit protection devices to both trade and end user customers.consumerunitworld.co.uk
Technically I believe they don't strictly comply with BS7671 when used in domestic because they are not shuttered though personally I think the interlock ones would be safe but you would be taking that engineering judgement on board if you fitted it.Client just bought new car and has been supplied with one of these, and wants a 32A commando socket fitted!
A 32A interlocked RCD protected socket has been asked for but do they comply?
I think this has been aired before but cant find any details so reviving this old post about EVCP.