What would everyone say the codes would be for the following:

1) tails 16mm not broken seals to check main fuse but if going on 100amp code c2 ?

2) old bar heaters in bathroom. code c1 ?

3) no supplementary bonding to pipe work at sinks in bathroom. code c3 ?

4) cracked socket code c2 ?

5) cooker circuit also feeding two sockets in up bedroom ?

any recommendations

Board has rcd protection to sockets, bar heaters but not to lighting or cooker circuit.

Thanks.
 
1. Cant code till you know for sure really , otherwise its just a guess.
2. Depends on if its in a zone , C2 if it is , C3 if its not.
3. If no rcd's for all bathroom circuits then code 2
4. Yes , C2
5. C2 if cables to sockets are in 2.5 or less , C3 for sockets having no rcd.
 
Last edited by a moderator:
1) Tails 16mm, I would LIM this as you cannot be expected to remove the fuse to check on an EICR, The DNO's think that 16mm on 100A fuses is just about OK anyway, (check the size of their service cable!)
2)I would C2 this if in a zone, c3 if not
3)C2, unless the readings between all Extraneous conductive parts and Cpc's of bathroom ccts. come out at less then 0.05 (usually means there bonded where you can't see)
4)C2
5)would depend on if the sockets are fused down or just direct spurs or spur on spur, if they are fused down no code (maybe observation), if they are a direct unfused spur no code (Observation) or if they are spur on spur in 2.5mm C2. If they are in 6mm or 4mm, No code.
 

Reply to eicr cding help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
674
Hi everyone Sorry if it's a repeated question tho. Agents followed me a failed visual EICR which has C2 for lack of RCD on cooker circuit and...
Replies
11
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
770
I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I...
Replies
29
Views
3K
First : here are 2 x sockets .What code would you give and why ? 3rd pick you can see rear thermal damage on double socket second : Roof...
Replies
32
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock