Gurnatronics

~
Trainee
How do you experienced testers do it. I’ve seen live to neutral LIM’d but Neutral to Earth and Live to earth showing >999 @ 500V. Surely pushing any voltage down a commoned neutral with live components on other circuits is asking for trouble, even at say 250V? I am 99% certain they don’t pull the neutral from the bar first as nothing is ever labelled. Am I missing something?
 
IR tests are dead tests. They should be done at the end with the installation complete, so you pick up if e.g. you've snagged a cable with a light switch screw.

So 99.9% of the time, unless I'm investigating a fault on a specific given circuit (and I know the installation very well ) I turn the main switch off for any IR tests.

For either the whole board, one side of the board, or a final circuit (board switched off in all cases) joining the line to neutral, and testing the cpc bar is an adequate test to ensure there are no earth leakage issues. For an EICR or pre-CU change this will be fine.

Some people do indeed take a shortcut and clip the N bar to a single outgoing Line conductor, and test this combination to the CPC bar. This will work, but can 'find' N-E faults on other circuits, and you then end up removing every Neutral anyway to identify where the fault is. So I don't advise this! They certainly can't do this with the board energised, and most MFT's would be screaming at you that you've lost the plot anyway.

If for any reason I'm exceptionally IR testing a single circuit with the board live, (a practice which would instantly fail any exam) I disconnect the Neutral, and make triple sure it's the right one.
 
That’s what I though. Surely with the main switch still on, they would be picking up a connection back at the transformer anyway when doing a N-E…?
Yes.
Some manufacturers let you do IR tests on the outgoing RCBO terminals, and it's easier to forgot to throw the main switch on an RCBO board. If the RCBO is single pole then exactly as you say, you pick up the upstream N-E link.
 
So, fairly safe to say most EICRs on critical power boards showing IR readings are full of crap then? 😂
Yea it’s difficult if you can’t isolate the DB.
I’ve said before clamp a earth amp meter around the Live conductors, to find the earth leakage current, then use ohms law to find the resistance
 