IR tests are dead tests. They should be done at the end with the installation complete, so you pick up if e.g. you've snagged a cable with a light switch screw.
So 99.9% of the time, unless I'm investigating a fault on a specific given circuit (and I know the installation very well ) I turn the main switch off for any IR tests.
For either the whole board, one side of the board, or a final circuit (board switched off in all cases) joining the line to neutral, and testing the cpc bar is an adequate test to ensure there are no earth leakage issues. For an EICR or pre-CU change this will be fine.
Some people do indeed take a shortcut and clip the N bar to a single outgoing Line conductor, and test this combination to the CPC bar. This will work, but can 'find' N-E faults on other circuits, and you then end up removing every Neutral anyway to identify where the fault is. So I don't advise this! They certainly can't do this with the board energised, and most MFT's would be screaming at you that you've lost the plot anyway.
If for any reason I'm exceptionally IR testing a single circuit with the board live, (a practice which would instantly fail any exam) I disconnect the Neutral, and make triple sure it's the right one.