Come across this a couple of times recently whilst doing eicr’s. Everything all ok except there is no access to the (presumably) earth rod. The cable just disappears under a patio.

Of course it may not even be an earth rod. It could be a plate or something. I’ve been giving these a C3 as I don’t know how reliable the connection is to the rod without being able to inspect it. Perhaps it should be FI though. This would then require lifting of the patio, which is perhaps a bit extreme given the ze is very good.

One of them had a very recent consumer unit change that looked to have been done very well. Should they have addressed the accessibility to the rod as part of this? I’m really not sure.

Another one is fire rated downlights. In most houses the ceiling is not considered a fire barrier, but it may be in flats/3 storey houses etc depending on how they are constructed. Either way imo it’s not a matter of electrical safety, so no code. I may note it on the report with no code though if I think any downlights are piercing a fire barrier and should be fire rated. Thoughts?
 
I'd say if you are getting a reading on rod, C3 and recommend rcds on all circuits or find earth connection plate

As for fire rated fittings, if bedroom above must be fitted C3 or observation maybe
 
There’s nothing in bs7671 about downlights as such but 527 deals with sealing of fire segregated compartments, if a fire barrier is penetrated, it needs to be suitably sealed, most homes are a single compartment and more often and not, fire rated downlights are not required.
Building regulations may require them tho but that’s not really a bs7671 issue.
 
  • Like
Reactions: timhoward

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

mattg4321

Arms
~
Joined
Location
South East UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
EICR code for inaccessible earth rod
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
mattg4321,
Last reply from
loz2754,
Replies
4
Views
5,144

Advert