Discuss EICR code for inaccessible earth rod in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

mattg4321

-
Esteemed
Arms
Reaction score
2,046
Come across this a couple of times recently whilst doing eicr’s. Everything all ok except there is no access to the (presumably) earth rod. The cable just disappears under a patio.

Of course it may not even be an earth rod. It could be a plate or something. I’ve been giving these a C3 as I don’t know how reliable the connection is to the rod without being able to inspect it. Perhaps it should be FI though. This would then require lifting of the patio, which is perhaps a bit extreme given the ze is very good.

One of them had a very recent consumer unit change that looked to have been done very well. Should they have addressed the accessibility to the rod as part of this? I’m really not sure.

Another one is fire rated downlights. In most houses the ceiling is not considered a fire barrier, but it may be in flats/3 storey houses etc depending on how they are constructed. Either way imo it’s not a matter of electrical safety, so no code. I may note it on the report with no code though if I think any downlights are piercing a fire barrier and should be fire rated. Thoughts?
 
I'd say if you are getting a reading on rod, C3 and recommend rcds on all circuits or find earth connection plate

As for fire rated fittings, if bedroom above must be fitted C3 or observation maybe
 
There’s nothing in bs7671 about downlights as such but 527 deals with sealing of fire segregated compartments, if a fire barrier is penetrated, it needs to be suitably sealed, most homes are a single compartment and more often and not, fire rated downlights are not required.
Building regulations may require them tho but that’s not really a bs7671 issue.
 
no access to the (presumably) earth rod. The cable just disappears under a patio.
You may find this similar thread helpful:

 

Reply to EICR code for inaccessible earth rod in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
410
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
951
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock