Hi All,
Many of you have been assisting me with a different EICR issue. Your contribution has been invaluable.
This post is not related to that.
I had an EICR undertaken on an installation which has a 4 year old CU with 9 circuits and RCD's. This was failed due to the following:
No continuity on CPCs of socket circuit. Remaining socket circuit has no continuity on lives or CPCs. Investigation required into socket circuits as cable is undersized for circuit breaker due to no continuity.
To set expectations, I have never worked on a CU but done plenty of tasks with other parts of the residential circuit. I am also the proud owner of a Fluke T130 (with display), plug-in socket tester, fluke voltage stick and some other electrical tools. I am a DIY'er.
My question:
With the self imposed constraint of not wanting to work on the CU, would it be helpful to open each socket on the Ring and check the live cables (at least 2 on each socket unless it is spurred?) and see where I locate a dead live cable (using voltage stick and 2 pole tester)? Presumably this will indicate where the Live continuity is broken? Perhaps, I will even find a loose Live cable connection to solve this particular problem?
Secondly,
Can I use the plug in tester along with opening up each socket to try and locate the broken Earth circuit? I am struggling with this as unless I find a disconnected earth cable, I am unsure on how I will be able to locate this.
I have seen videos where you expose the tails on the CU end and use that to troubleshoot but ideally, would like to avoid this as I have never worked on a CU.
I am happy to invest in a multi-meter (My 2 pole tester does have a voltage display) if that is essential and would appreciate your advice with this please. My aim is to fix the issue and then repeat the EICR with a better outcome.
Thanks in advance
I’m afraid it’s not a job for a diyer.
it’s a dead test, using a continuity tester, a hobby type multimeter won’t cut it across the lengths of cable needed.
what you could do easily is, power off, unscrew each socket and see if there’s a loose cable behind any of them.
This would explain no continuity, but if that doesn’t flag up a problem, the break could be on a cable between sockets.... meaning it’s been damaged somehow and would need repaired/ replaced.
if it's a ring, loss of continuity will not lead to part of the circuit being "dead". afraid it's as little spark says, a job for a competent sparks.
you could post your rough location. one of us may be close enough to sort it at a sensible cost.
so you're basically down to visual inspection at sockets. conductor/s come out of terminals is about as far as you can go short of having accurate meter/s that can measuer the resistance of a few yards of copper cable and a spark deduce where the break/s are. we're talikg of fracrions of an ohm. most multimeters can't go that low.
I wasn't expecting part of the circuit to be dead as presumably it is being powered by the other "connected" part of the ring. I was hoping to find one leg of the ring that is dead and that may help me track down where the link is broken. Plausible?
Also on the earth break, assuming this isn't just loose in one of the sockets, can I use a really long piece of wire and join it to different parts of the earth socket to check continuity? I can do continuity on my current 2 pole tester. I appreciate that this will need some guestimates on the sequence of sockets on the ring.
you'd need to power down and safe isolate . then with both legs dissed from the CU. long lead from socket to socket on each conductor of each leg.
Please excuse my ignorance but for the Live break, can I not rely on the method I mentioned in the previous response and use that to track down where the break might be?
For the earth break - assuming it isn't just a loose wire at the back of a socket - I'd need to use this long cable method in conjunction with my two pole tester. Have I understood correctly?
Reply to EICR Failure - lack of continuity in the UK Electrical Forum area at ElectriciansForums.net
So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a...
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...