done that a few times. sometimes a quick solution. trouble is, we sometimes tend to overthink things trhese days, doing it by the book. back in the 15th era it was a quick blast of the wind-up megger, then the bang test.
 
Thanks for all the suggestion guys.
Another thought: let's assume that I am over thinking this (not the first time!) and the issue lies at the back of one of the sockets in the form a loose cable in the terminal, I was wondering how I would verify this.

Could I start by safely isolating the circuit, removing one of the sockets on the RFC and placing the probes of my 2 pole tester on the two ends of Live and then the same on Earth. Presumably this will not report continuity at this point? As a further test I could do the same on neutral and that should report continuity as the EICR hasn't said otherwise.

Once the above has been established, I could run around all the sockets and look for the loose cable. Once found and resolved, I can repeat the above test and expect to see continuity.

Is this plausible?
 
i think the easiest course with limited equipment is to diss 1 leg of the ring (L,N,&E) in the CU. power up the connected leg then use socket tester round the sockets. repeat for other leg. observing safe isolation before sticking fingers in anywhere.
 
Related to the above, is it the case that if I was using my Fluke 2 Pole tester on a socket across L and E and if unknown to me, the earth continuity was broken further up the ring chain, my 2 pole tester will not detect power at the socket I am testing?
 
Related to the above, is it the case that if I was using my Fluke 2 Pole tester on a socket across L and E and if unknown to me, the earth continuity was broken further up the ring chain, my 2 pole tester will not detect power at the socket I am testing?

If you haven't disconnected anything prior to testing, then there will be earth continuity from the other leg and therefore you will get voltage between L and E at the socket. So you may well miss the broken earth fault.
 
Aha and if I were really unlucky and have an earth break in both directions? Just trying to establish a principle.
If both earths were incomplete then you would get full voltage between L and N, but either no voltage, or inconsistent voltages L to E.

That only shows that an earth is present (or not) though, not necessarily a continuity of earth conductors back to the main earth terminal.

That's why dead testing is carried out to check the continuity of the 'ring'.

The continuity setting and reading on the Fluke T130 can give you a basic idea and can be used to confirm that there is no continuity (or that there is some sort of continuity). but for a proper test with the accuracy required for certificates, etc - then a low resistance ohmmeter is required. (Or a Multi Function Tester that includes that, which is the usual equipment electricians have)
 
Thanks for the explanations @Dartlec.
I appreciate that to do proper continuity testing, I would need additional equipment. That's quite understandable.

I just wanted to understand the reliability of my 2 pole tester when I am about to work on a circuit. I replaced my fluke voltage stick on the understanding that the two pole tester is the most reliable. Presumably this is only the case, if we have continuity on Earth/Neutral (on at least one leg of the ring). If there is no continuity on E/N, the tester would report no power but I could potentially get a belt from the live when I touch it as it is hot.

Have I understood this correctly and/or if this a very far fetched situation? Perhaps in reality testing across L N and L E is adequate.

I would appreciate your thoughts on this.
 
Thanks for the explanations @Dartlec.
I appreciate that to do proper continuity testing, I would need additional equipment. That's quite understandable.

I just wanted to understand the reliability of my 2 pole tester when I am about to work on a circuit. I replaced my fluke voltage stick on the understanding that the two pole tester is the most reliable. Presumably this is only the case, if we have continuity on Earth/Neutral (on at least one leg of the ring). If there is no continuity on E/N, the tester would report no power but I could potentially get a belt from the live when I touch it as it is hot.

Have I understood this correctly and/or if this a very far fetched situation? Perhaps in reality testing across L N and L E is adequate.

I would appreciate your thoughts on this.

It is essential to do appropriate testing. Splitting the ring and doing end to end tests with a proper low resistance test meter is a vital one.

A 'proper' tester will test resistance with a 200mA test current and give accurate results.
 
Thanks for the explanations @Dartlec.
I appreciate that to do proper continuity testing, I would need additional equipment. That's quite understandable.

I just wanted to understand the reliability of my 2 pole tester when I am about to work on a circuit. I replaced my fluke voltage stick on the understanding that the two pole tester is the most reliable. Presumably this is only the case, if we have continuity on Earth/Neutral (on at least one leg of the ring). If there is no continuity on E/N, the tester would report no power but I could potentially get a belt from the live when I touch it as it is hot.

Have I understood this correctly and/or if this a very far fetched situation? Perhaps in reality testing across L N and L E is adequate.

I would appreciate your thoughts on this.
In general a 2 pole tester such as your T130 is considered the best way to check for voltage as it is more reliable.

You are right that if in theory there was no continuity on E AND N, that you might get no result. That is a fairly unlikely event though.

Although if I recall correctly, the T130 does also indicate when held to a "Live" wire with just the main probe - so it combines one of the benefits of the voltage stick.

It is one of the reason that any 'work' should always be done on a dead circuit though. Live testing is only for probing at the terminals of a socket - and really the main purpose of a voltage indicator like the Fluke is to prove dead to work safely...
 
In general a 2 pole tester such as your T130 is considered the best way to check for voltage as it is more reliable.

You are right that if in theory there was no continuity on E AND N, that you might get no result. That is a fairly unlikely event though.

Although if I recall correctly, the T130 does also indicate when held to a "Live" wire with just the main probe - so it combines one of the benefits of the voltage stick.

It is one of the reason that any 'work' should always be done on a dead circuit though. Live testing is only for probing at the terminals of a socket - and really the main purpose of a voltage indicator like the Fluke is to prove dead to work safely...

My Kewtech does the same, ie single probe testing. Obviously for testing for dead you should use the 'proper' two probe test though. I'm not sure having the single probe test is such a good idea
 