Thanks for the explanations
@Dartlec.
I appreciate that to do proper continuity testing, I would need additional equipment. That's quite understandable.
I just wanted to understand the reliability of my 2 pole tester when I am about to work on a circuit. I replaced my fluke voltage stick on the understanding that the two pole tester is the most reliable. Presumably this is only the case, if we have continuity on Earth/Neutral (on at least one leg of the ring). If there is no continuity on E/N, the tester would report no power but I could potentially get a belt from the live when I touch it as it is hot.
Have I understood this correctly and/or if this a very far fetched situation? Perhaps in reality testing across L N and L E is adequate.
I would appreciate your thoughts on this.