Related to the above, is it the case that if I was using my Fluke 2 Pole tester on a socket across L and E and if unknown to me, the earth continuity was broken further up the ring chain, my 2 pole tester will not detect power at the socket I am testing?

If you haven't disconnected anything prior to testing, then there will be earth continuity from the other leg and therefore you will get voltage between L and E at the socket. So you may well miss the broken earth fault.
 
Aha and if I were really unlucky and have an earth break in both directions? Just trying to establish a principle.
If both earths were incomplete then you would get full voltage between L and N, but either no voltage, or inconsistent voltages L to E.

That only shows that an earth is present (or not) though, not necessarily a continuity of earth conductors back to the main earth terminal.

That's why dead testing is carried out to check the continuity of the 'ring'.

The continuity setting and reading on the Fluke T130 can give you a basic idea and can be used to confirm that there is no continuity (or that there is some sort of continuity). but for a proper test with the accuracy required for certificates, etc - then a low resistance ohmmeter is required. (Or a Multi Function Tester that includes that, which is the usual equipment electricians have)
 
Thanks for the explanations @Dartlec.
I appreciate that to do proper continuity testing, I would need additional equipment. That's quite understandable.

I just wanted to understand the reliability of my 2 pole tester when I am about to work on a circuit. I replaced my fluke voltage stick on the understanding that the two pole tester is the most reliable. Presumably this is only the case, if we have continuity on Earth/Neutral (on at least one leg of the ring). If there is no continuity on E/N, the tester would report no power but I could potentially get a belt from the live when I touch it as it is hot.

Have I understood this correctly and/or if this a very far fetched situation? Perhaps in reality testing across L N and L E is adequate.

I would appreciate your thoughts on this.
 
Thanks for the explanations @Dartlec.
I appreciate that to do proper continuity testing, I would need additional equipment. That's quite understandable.

I just wanted to understand the reliability of my 2 pole tester when I am about to work on a circuit. I replaced my fluke voltage stick on the understanding that the two pole tester is the most reliable. Presumably this is only the case, if we have continuity on Earth/Neutral (on at least one leg of the ring). If there is no continuity on E/N, the tester would report no power but I could potentially get a belt from the live when I touch it as it is hot.

Have I understood this correctly and/or if this a very far fetched situation? Perhaps in reality testing across L N and L E is adequate.

I would appreciate your thoughts on this.

It is essential to do appropriate testing. Splitting the ring and doing end to end tests with a proper low resistance test meter is a vital one.

A 'proper' tester will test resistance with a 200mA test current and give accurate results.
 
Thanks for the explanations @Dartlec.
I appreciate that to do proper continuity testing, I would need additional equipment. That's quite understandable.

I just wanted to understand the reliability of my 2 pole tester when I am about to work on a circuit. I replaced my fluke voltage stick on the understanding that the two pole tester is the most reliable. Presumably this is only the case, if we have continuity on Earth/Neutral (on at least one leg of the ring). If there is no continuity on E/N, the tester would report no power but I could potentially get a belt from the live when I touch it as it is hot.

Have I understood this correctly and/or if this a very far fetched situation? Perhaps in reality testing across L N and L E is adequate.

I would appreciate your thoughts on this.
In general a 2 pole tester such as your T130 is considered the best way to check for voltage as it is more reliable.

You are right that if in theory there was no continuity on E AND N, that you might get no result. That is a fairly unlikely event though.

Although if I recall correctly, the T130 does also indicate when held to a "Live" wire with just the main probe - so it combines one of the benefits of the voltage stick.

It is one of the reason that any 'work' should always be done on a dead circuit though. Live testing is only for probing at the terminals of a socket - and really the main purpose of a voltage indicator like the Fluke is to prove dead to work safely...
 
In general a 2 pole tester such as your T130 is considered the best way to check for voltage as it is more reliable.

You are right that if in theory there was no continuity on E AND N, that you might get no result. That is a fairly unlikely event though.

Although if I recall correctly, the T130 does also indicate when held to a "Live" wire with just the main probe - so it combines one of the benefits of the voltage stick.

It is one of the reason that any 'work' should always be done on a dead circuit though. Live testing is only for probing at the terminals of a socket - and really the main purpose of a voltage indicator like the Fluke is to prove dead to work safely...

My Kewtech does the same, ie single probe testing. Obviously for testing for dead you should use the 'proper' two probe test though. I'm not sure having the single probe test is such a good idea
 

Reply to EICR Failure - lack of continuity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a...
Replies
32
Views
888
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
296
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
759
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
898
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock