Converting a broken ring into two radials without investigating the break is not acceptable. If the break is as the result of a screw through the cable, then there will still be the possibility of a live screw somewhere, even after the the breaker has been downrated.
None of this comes under the scope of an EICR. The fault gets a C2 as a minimum, and if a wander around with a voltage detector finds a live screw, or a screw in a 'safe zone', then it's a C1.
Fault rectification comes later, and if the decision is taken to split the ring into two radials is made, then the section of cable with the fault needs to be identified and completely disconnected at both ends.
Personally this bit would of worried me .
So, RN tested out fine, but R1 - open circuit, R2 - open circuit ! Oh joy. At this point the current tenant piped up and said "Should I have mentioned some of the sockets were getting hot ?!"
Just seen an image of a damaged cable and the body of a mouse, and it's made me remember a throw away comment from the tenant that they've had mouse issues. Just shows how important it is to listen to the occupier as well as doing the inspection. I admit that just didn't register with me.
I can see the arguments for and against a C2 or FI in this case. I've found a fault and know what it is, but currently I don't know where it is or the fix to put it right, so the first bit is a C2, but it's also an FI because I don't know why the fault exists. However I've only been paid to do the EICR not to fix, so you could say I've provided the information necessary for another sparky to investigate and fix, so yes I can see a C2 would be right. I do wonder if the FI status should be scrapped to be honest.
I disagree @Paignton pete and @buzzlightyear
This is an inspection only.
there is no further investigation required, a fault has been found in 2 conductors of a ring.
report it's condition as C2 and move on.
if it was not a ring, and the cpc was broken, It may well be a C1, no further investigation is required to find where it is broken. just report it and move on.
Obviously to fix the fault will require further investigation (AKA Fault Finding) as it has not been precisely located.
You can't report a C1 and move on you either have to fix it there and then or isolate that circuit. I have just today been to a job that someone else has inspected (eicr) and failed because there was no end to end continuity on house sockets r1 and rn but cpc was ok, I was asked to attend and fix the fault the other tester found. (I found the fault it was an incorrectly terminated spur unit) however this fault led to severe thermal damage on two of the sockets worse I have seen in a long time to be honest, back of skts melted away another day or 2 and this could of been much worse. This gave cause of concern to me as should the electrician who tested this leave the property knowing there was no continuity on the ring and knowing this can lead to excessive overload on the circuit
Looks like that's had loose connections.
It all comes back to whether is a C1 or not.
if you deemed it to be a C1 you have to either correct it or dont re energise it.
any other code, yes report and move on. You are not there to make alterations additions or repairs. You are 5here to report on the condition of the installation at the time of testing.
obviously an FI could be an immediately dangerous situation after further investigation, but at this stage before you investigate you won’t know because you haven’t looked into the fault yet as that’s not what you are there to do.
You can’t criticise a sparky who fails to identify an immediately dangerous situation in a circuit if they have classed that circuit as FI. they have identified something is wrong but would need further investigation to know if it’s a C1 or C2.
Here's one I wasn't expecting on an EICR. Recently rewired and renovated 2-bed property (2015ish). Having an EICR as a new tenant to move in soon. No reported problems.
I expected to be in and out in about 3-4 hours to be honest, and as expected I found nothing wrong until I began my ring final tests. All the sockets had already tested fine during my visual check and quick test with my Kewtech tester. I was a little surprised to find this property only had the one ring with the combi boiler also hanging off it, given the board was a 10-way with 4 spare ways in it. Made me wonder why during the rewire the property wasn't split into an upstairs and downstairs ring, but anyway....
Anyway according to the Codebreakers guide I should be giving this a C2 (Actually I'm thinking of giving it an FI), and handing the report to the landlord. I admit I don't get many outright failures, but this one obviously is.
Anyway what I was going to ask is I'm assuming what I have here is a ring that's functioning as 2 overloaded radials, and somewhere both conductors have a break in them (It'll be just my luck that they will be in different locations). It can't be classed a C1 can it, as this fault could have been there for years, and another couple of days shouldn't hurt. What would you classify this as - C1, C2 or an FI ?
Broken ring, sockets getting hot. 20 A accessories on 32A breaker? Fire risk. F1
An open circuit on any conductor on a ring final circuit should attract a C2. What limitations are preventing you inspecting and testing thus giving an FI code?
The FI code is massively misunderstood and misused, it should be used when a limitation in the inspection prevents you from assessing something and where did to the limitations, you suspect danger or potential danger.
I am going to disagree and advise that you should base the answer on your findings as your initially there to carry out a condition report. If you test a circuit and find there is no conrinuity of CPC and the problem is not starimg you in the face, then you write down FI in order to advise the client as per your findings. If you see a break in cable and again your remit is to report findings then you add C2 to the report. If however, your remit is to report and resolve then you write the code that applies. There is no science and secret behind codes. The issue is people reading too much into a simple task. C1 dangerous, C2 is potentially dangerous, C3 advisory and FI further investigation to determine result.
I disagree, if open circuit has been confirmed on RFC then rectification is the next step not FI surely.?
The answer is in the last two letters of the acronym 'EICR'. If you're tasked with repairing anything you find, then any issues you resolved won't be coded - if you find a fault and can't repair it, then you report on the condition of the installation at the time of writing.
Exactly! Repairs are not in the remit of an EICR, although myself and most others will deal with very simple faults to repair as they go. Bit like the MOT test for your car, when the tester sticks on a new wiper blade or changes a brake light lamp to avoid failing the car.
my garage issue a fail cert for a faulty lamp
even though i tell them if it needs lamps or brake pads etc, just to do it and send me the bill.
normally i get
fail cert
invoice for number plate lamp etc.
pass cert
i suppose it is the correct way of doing it and also stops the garage from having an unusual pass/fail ratio that might lead them to being checked for irregular practices.
edit, that leads me on to, why dont the part p scams, keep an eye on members that have unusual ratio's of satisfactory vs unsatisfactory eicr's and look closely at the ones who are passing nearly 100% of certificates issued?
Reply to EICR - No Line or CPC Continuity on Ring in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...