First periodic test since doing my 18th edition top up months ago and I don’t have it t hand. So until I get home to have a nose and realise this question is ridiculous I need reminding.
3 circuits (lights x 2 and boiler ) are not on an RCD. The installation is over 10 years old as the last inspection date was 2006.
Do I -
- Record this as an action.
-Modify to existing regs and put them on an RCD.
- Do nothing as at time of install it was ok.
Thank you gents
Do I -
Thank you gents
Regulations are not retrospective Scott.
Lights on an RCD in dwellings are a requirement now,so should be coded accordingly (most likely code 3) boilers are not, unless there is another reason such as installation method. Do not fall into the trap of thinking everything must be on an RCD .
As above, you will have an observation for AC final circuit supplying luminaires in domestic (household) premises not protected by a 30mA RCD.
You will also likely have a similar observation for cables concealed within a wall at a depth of less than 50mm not protected by a 30mA RCD.
Do I -
Thank you gents
Remember a inspection report is a snap shot in time and only observational findings and rudimentary testing
You do not start alterations or remedies until ‘after’ you have compiled your report
So no you don’t alter anything during the eicr
Another factor to consider is circuits, including lighting, in the bath/shower room. According to the Electrical Safety Council's Best Practice Guide 4, they need to be RCD protected, or full supplementary bonding needs to be in place, otherwise it's a C2.
Reply to EICR Test and tips thank in the UK Electrical Forum area at ElectriciansForums.net
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
I am a 57 grumpy old bloke called Karl (only grumpy when I'm tired lol) and worked with electric all my life, well at least since I remember, I...
Priced to do kitchen electrics & mains board upgrade for someone a while back, they accepted my price. I explained that the mains needed changed...
Hi All I’m in charge of the maintenance (machinery and facilities) in a plastics manufacturing business. I have a ‘team’ of little old me and an...