Carried out an EICR today few things noted down to do,there is a 10mm equipotential bond on water and gas services. BUT the gas is bonded at the meter under the stairs and 2 inches down it enters the solid floor. also in the lounge there is a small gas pipe that comes out the wall to the fire and a pipe that comes out the wall in the kitchen to the cooker, my question is do i tell customer each point were it comes out in the rooms it needs a 10mm earth bond.
or would you guys ignore it cause its earthed at the gas meter.
i had an assessor raise the reg on corrosion to pipes on a new build but this time its not a newbuild and suppose this is relative to what he said.

kind comments only lol
 
Do a wandering lead earth continuity test where the pipes are accessible if your really worried
 
but don't use a nail in the pipe to get your croc clips on
 
I think your assessor is talking out of his ars*
It has to be bonded per regs , talk of corrosion is neither here nor there.
 
Carried out an EICR today few things noted down to do,there is a 10mm equipotential bond on water and gas services. BUT the gas is bonded at the meter under the stairs and 2 inches down it enters the solid floor. also in the lounge there is a small gas pipe that comes out the wall to the fire and a pipe that comes out the wall in the kitchen to the cooker, my question is do i tell customer each point were it comes out in the rooms it needs a 10mm earth bond.
or would you guys ignore it cause its earthed at the gas meter.
i had an assessor raise the reg on corrosion to pipes on a new build but this time its not a newbuild and suppose this is relative to what he said.

kind comments only lol

I suppose this assessor also requires that where any plastic water pipe is installed a bond is required if it changes to copper again!
 
There could be concerns if the pipe was entering the building at various points, rather than emerging from the structure at more than one place

Extraneous definition = existing on, or coming from the outside
 
True , but in a domestic scenario , its not an issue.
I have to say though that some of these scheme inspectors spout mucho nonsense.
 
As biff says, cont check if you are concerned.
As yellow says, bonding last of your worries if corrosion has severed the pipe...
 