so are we all done here then?! we've now established that the OP is now not worried and has read the maths that verifies what we've told him. hopefully him and the mrs can enjoy a nice meal this evening :)
Haha cheers dan, doesnt help when my mrs has some ocd and worrys, iv since spoken to an electrician who will put a 40a mcb in my board to cover any nuiscance tripping he said, so at least thatll make her feel like something has happend and will ease her mind but i know now its fine to use as it is
why fit a 40A when the 32A is not tripping????? depending on the installation method of the 6.0mm cable, a 40A may be too high a rating for the cable.
Really???
Dave has done the maths and showed you that the 32A MCB is fine. As Tel says, a 40A MCB is probably too high for the 6mm cable, depending on the installation method. This will make it more dangerous, not safer!
we cant blame a bloke for getting a little confused over his oven... its not familiar territory. If the TV was playing up, or xbox went down, the tools are out, the experts are in.
Stop right now. The "electrician" you have consulted is, at best, having your pants down and at worst is a clown.
Why bother upping the breaker when the existing one is not tripping? Your wife may have OCD but you are listening to the wrong advice, installing a 40 amp MCB will not decrease any danger but will in fact increase it
Unless the entire cable run of your 6mm is clipped direct, then a 40amp breaker will exceed its current carrying capacity. Can you provide accurate details of how the cable has been run (if i have missed that on the post already i apologise) but as Trev has rightly said, leave the 32A in. Why change something that is clearly not causing an issue.
Lets say its been installed to Red meth100, then you will be able to carry 32 amps max down that 6mm, a deviation of 8 amps between the breaker and cable max,which will cause a significant build up in heat in the cable before the breaker throws. If your wife suffers from OCD, she will have a hell of a time getting her head around the house when its a pile of ash and rubble.
stick a 4 pole breaker in. that'll fix it. LOL. :shout:
Ah so a old spark gives me worrying sugguestions, i phone a qualified spark and he gives me the wrong advice?! I dont know what to do then, can i get someone out to so some kind of load tests or anything on it, ive been happy with it from the start and everythin was hunky dory till then.
And in regards to it not tripping the oven/ hob as only been tested shortly to see if everything heated up etc which it did no problem
stop worrying. you have had loads of posts telling you it's OK as it is.
This thread is now pointless
Once more in case the message by some fluke gets taken at its word
It is fine,leave it alone.leave the mcb alone,leave the cable alone,if she is that paranoid after pages of reassurance,leave the wife
Also didnt mention dont know if it matters now tho... The oven is on a 13 amp plug going into a double socket then going into a cooker fuse (with a socket on)
Thank you all anyway for the mixed reactions & advice
Even with it on a plug top you will be unlikely to blow the fuse in the plug, and even if you did it is safe and would just need a new fuse.
I would probably recommend not using a kettle / toaster and the like in the socket on the cooker switch as well as using the cooker. The cooker on its own will be safe at all times and will not blow the fuse in the plug in most cases.