Hi, ive just installed an electric shower at work (industrial site) its a 10kw shower and ive used 10mm cable with an RCD for protection. Another electrician on site has passed comment that you need to install the same size earth as the live and neutral? ive never heard of this but it maybe a requirement of the new regs?

does anyone know this answer?

Cheers Dave
 
It's not needed to be the same size, providing that by Adibiatic equation proves the smaller CPC will be sufficient

Did he tell you why it needed to be the same size? Are you working to a set of reguations outside of the BS 7671-2008, that specifies all CPC's need to be the same size as the live condutors?

Seems like you never used T+E but singles, but the CPC for a T+E is 6mm
 
thanx for that Malcolm, yes its installed with T+E and like you have confirmed i always thought the CPC in T+E as been installed with the Regs in mind was sufficient as a CPC. ive never come across installing a same size earth as the live + neutral when using T+E, but yes when using singles all conductors tend to be the same size.

cheers Dave
 
I would ask him he if wants to do the job, No I thought not. Why is everybody an expert when looking at other peoples work.

Ask him to explain the reason why? Probably heard it of a mate who's mate is an NIC electrician lol
 
Sounds like the sort of bloke who would send you to the stores for tartan paint.
Just thought is he getting confused with exporting PME, is the shower in a seperate building to the point of supply?
 

Reply to Electric Shower install in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock