Discuss Electrode heaters own circuit in the Australia area at ElectriciansForums.net
S
SimpleSimon
Anyone tell me if there's a regulation that says water heater electrodes have to be on their own dedicated circuit?? Ive thought this for years but now cant see the reg. Looked all through chapter 554 cant see it.
Sent from my GT-I9100 using Tapatalk
There isn't one Simon the same as there isn't one for a conventional water heater.
The guidance notes, forget which one now recommends that a heating vessel of >15 litres should be on it's own circuit.
Appenix 15 tells us that these types of equipment should not be feed via a ring main.
About the only reg that will guide is perhaps regulation 510.3 where it tells us of manufacturers instructions
There's always confusion between immersion heaters and electrode boilers, are you sure this is an electrode Simon?
That was what i was thinking Malcolm. Knew id seen something but forgot about the guidance notes. Thanks.
Ill explain the situation.
Zip tap on a 13a FCU sharing a radual with 20a MCB(shared with outside lights)
doing a rewire in the kitchen. New cooker going in which is 6.7Kw previously ut was a gas cooker so wired into ring. Now the new cooker needs it's own circuit. What i want to do is get rid of water heater/lights radial and replace this space for new cooker otherwise it would mean changing board. (no space)
Im thinking zip tap can go onto new kitchen ring as its a small water heater though cant sew the exact Kw.
I was just checking the reg for the specifications to see if it definetky needs its own circuit.
Ah right, the Zip Taps go from 1.5kW up to about 6kW, maybe remove the cover and it'll be written inside?
OSG, 8.5; EGBR 4.5 and GN1, C4 advise "Water heaters fitted to storage vessels >15 litres ... should be supplied by their own separate circuit."
Reply to Electrode heaters own circuit in the Australia area at ElectriciansForums.net
Evening all 🙂 I have been asked to quote for installing infrared heating panels (smart) throughout a house. This will be a first for me and I...
4K
Someone wants me to put a water heater(30 amps), range(40-50 amps) and dryer(30 amps) all on a single 60 amp circuit. I said that's a bad idea...
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
  • Locked
5K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...