Is there any advice (not FCUs everywhere!!) that may help me defeat a plumber who intends to use part p to take this work?

is there any justification in using 2x10mm cables instead of my proposed 16mm or 25mm cable?

Any help would be appreciated.
 
Its funny that I have seen this post on here,

I done a similar job as part of an install not to long ago,

we used a 10mm cable twin and earth (grey one) in ducting.

Simple, three letters FCU. Avoids any consumer units so no need to notify anyone

Simples!! Hope this helps

How does fitting a FCU make it non notifiable? Also I'd love to see that 10mm terminated into said FCU.
 
If you have the regs you'll know that "showers" are notifiable - but I suspect you spend your money on feeding your horse.

Now that is funny! I thought Gyppo's had horses, the Polish have cabbage based food products?
 
Is there any advice (not FCUs everywhere!!) that may help me defeat a plumber who intends to use part p to take this work?

is there any justification in using 2x10mm cables instead of my proposed 16mm or 25mm cable?

Any help would be appreciated.
Err, remind the PLUMBER its an ELECTRICAL job and he should restrict himself to unblocking toilets?
 
Looking through our guide to the building regulations 2.1 design, can't find even a transparent reason for my choice of cable over his??

should meet the requirements of ADS.

Good client, could do with more decent work (new installs) like this one.

As always, appreciate the useful replies.
 
Looking through our guide to the building regulations 2.1 design, can't find even a transparent reason for my choice of cable over his??

should meet the requirements of ADS.

Good client, could do with more decent work (new installs) like this one.

As always, appreciate the useful replies.
If you do a search on here you'll find a NAPIT guide to exporting the earth? Doubt the plumber would have that knowledge?
 
Is there any advice (not FCUs everywhere!!) that may help me defeat a plumber who intends to use part p to take this work?

is there any justification in using 2x10mm cables instead of my proposed 16mm or 25mm cable?

Any help would be appreciated.

Start off by working out CCC of the 10mm t+e over 40m and see if you feel its ok, then you will have 2 x 4mm cpc conductors (pressuming that 2 x 10mm t+e are for 2 seperate supplies) do you think that this is adequate for any extraneous earthing that is possibly required? Still don't see how you can do this with no CU????????

Ask for the plumbers spec so you can price on a level playing field, then post it pls pls pls
 
Why is the plumber proposing ANYTHING, other than pipes and where he'd like the FCU for the boiler supply?
EXACTLY!!....didn`t we have something in here the other day about this kind of thing?....like plumbers gettin above their station.......
 
uhh what just happened? someone told op he should calculate supply cable size then he looks in a book and decides to use 10 mm as the plumer knows best?
 
tell this plumber to stick to the water, let the men do the really work, i dont now why the hell a did part p, with all elses dumb --- around, we have been to so many jobs were elses people think doing the pat p course make them a electrician
 
tell this plumber to stick to the water, let the men do the really work, i dont now why the hell a did part p, with all elses dumb --- around, we have been to so many jobs were elses people think doing the pat p course make them a electrician

You wouldn't find me messing with water or gas thats for sure
 
1. SWA has mechanical protection so a better option as you can eliminate the need for RCD protection on the sub main.
2. Do you want to extend the equipotential zone or make outbuilding stand alone TT. I personally would more than likely extend zone as its TN S and install EMT in outbuilding.
3. IMO a CU in the outbuilding is a must.
4. You need to calculate size of sub main and type and size of overcurrent protective device to meet disconnection times and volt drop.

Just a few points to get you thinking.
 
uhh what just happened? someone told op he should calculate supply cable size then he looks in a book and decides to use 10 mm as the plumer knows best?
looking at ops previous posts he has done cu changes etc etc i am starting to believe he is either someone ignoring part p and hasn't the knowledge an electrician should have or is himself a plumber and we are telling him how to do electrics?
 
I was told by a mate at the pub that as long as you dont create a new circuit by adding a CU then it isn't notifiable. Anyway the 10mm cable WAS too big to terminate so just a little bit of creativity with a connector block and some 2.5 twin and earth sorted that problem. Well notifiable or not at least it alleviates any need for testing as a simple functional test works and its all protected by a 13A fuse which is easy to replace, was nice enough to leave a small pack of them behind as about 3 of them went faulty when I turned the heater on so just left that off when i went to the pub at the end of the day with my cash. Simples
 