Discuss Extending tails - SWA or Hi Tuff ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Just wanted to know which people use.
My case.
Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this and will be greater than 3m from meter. Void above garage is used to route cables to main house so can use this to route cable for extension to tails from new switched fuse to consumer unit. A 25mm 3-core SWA is normally used, but its really inflexible, so whats to stop Hi Tuff being used instead ? I dont see anything in BS7671 that mandates the use of SWA for this.
Thoughts anyone ?
You could avail of a number of cable options, provided they're adequately protected. Can you be certain that no one would damage tuff sheath cable in that void, with only switchfuse protecting them?
SWA is cheaper than HiTuff type cables, and the difference can be quite a lot on the larger sizes. This is presumably due to the much higher demand for SWA.
SWA is often used because it is the traditional choice and is usually more readily available in most wholesalers.
Reply to Extending tails - SWA or Hi Tuff ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hey everyone, working on a new build house and outside garage is wired up like this, however customer wants a Garage Consumer Unit instead of the...
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
My sister has a cable feeding an outside boiler (see image). I want to tidy it up by adding a new piece of cable as shown. I can't see any ends...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
