J
jontykint
Hi
Some flats have been wired and since the 1st fix electric has been done, gas has been installed into the flats.
As this wasnt there as the wiring was carried out, there is no bonding to the incoming gas pipe in the flat.
There is no access to bond without major disruption within the individual flats.
The incoming gas main and manifold supplying 6 gas meters are in the cellar of the building.
The incoming electric main is also in the cellar, supplying 6 sub-mains which supply each flat in 3-core swa
Can the gas bonding for each flat be carried out according to regs at the Main Earthing Terminal in the cellar only?
Is there a way of making the incoming gas pipe at the flat non-extraneous so you do not require bonding??
Cheers
I would think this is ok if the sub main cable is capable of carrying the fault current as its 3 core presumably 16mm or over I would go that way.
the sub main is 3-core 25mm
so the earth from consumer unit to Main Earth Terminal is 25mm
so this can negate the need to bond incoming gas in the flat to consumer unit???
this could be a life saver
wonder hoe the NICEIC see this??
In the NIC 'Snags & Solutions' book on earthing & bonding, it reccomends bonding service pipes at point of entry to the main building and also point of entry to each subsequent flat.
I believe the diagrams used are taken from GN 8, as is most of the text accompanying them.
is there a solution for this snag then?!
that doesn't involve ripping out loads of new plaster ??
strictly speaking, this boils down to the definition of the word "installation". if each flat is to be considered an installation, then maion bonding needs to be cartried out at point of entry (or as close as) to each flat. If the building is to be classed as an installation, then main bonding only needs to be carried out at the origin of the gas supply into the building.
I believe that gas suppliers are now using a non metallic fireproof pipe for the final connection into houses. This means the pipe is no longer extraneous. If you could get some of this 'pipe' (if it exists) the main incomer could be insulated and also the connection into each flat.
But don't get your hopes, up I could be mistaken, try asking in a boiler forum.
Otherwise, main bonding is the only solution and further bonding (apart from gas) maybe required in the flats..
Technically should be bonded at the point of entry to each flat as already stated. However if you prove the pipework is electrically continuous from the meters at the intake to each flat I cant see that bonding each service at the intake would be a problem. Continuity results should be recorded on the EIC's and a notice should be provided at the intake stating that following any alterations to gas pipework a test of the effectiveness of main bonding to flats should be carried out.....thats my take on it.
Sounds common sense to me.
Thats the best and most logical way round the problem. If the supply pipe form the meter to the flat is insulated/non conductive then its time for a rethink.
Hi
Cheers
Hang on a minute here, ....Are you telling us that there was no drawing that you were working too?? Does that mean, the only reason the main water pipe was provided with a means of bonding, is because it was installed prior to the first fix electrical??...
Now everyone's scratching heads trying to circumvent the requirement of BS7671!!! As far as i'm conserned, if this supply gas pipe to individual apartments is copper, then someone has got to bite the bullet and take the hit, ...and install that bonding cable to these gas pipes, as it should have been in the first place. The only other alternative that i can see is, if the gas point is in the vicinity of the water bonding point, it is then permissible to link the two systems back to the MET on a single bonding cable...
think of this in a commercial situation, or industrial. Say you have a factoryu with many different rooms, and floors, but all in the confines of one building, then you wouldnt bond the pipes at the entry to every room would you? now substitue the rooms for flats, and its no different. the only problem may be access for any future spark to the buildings MET and switchroom
Those rooms wouldn't have a DNO supply in them either would they?? Every separate metered DNO supply ''installation'' Should also have any main service pipework or metalwork bonded as it enters the sub division of the building. It's clearly a requirement, ....so end of!!! lol!!!
Just like to add a comment that reinforces the need to bond at the point of entry that you may want to add to the mix.
The situation with the gas pipe will likely change through the life of the building. Mods added, pipes chopped, boliers changed and different supplies provided. If the pipes are not bonded at the point of entry you can't guarantee against the risk of a dangerous potential entering the flat. Hope this helps - good luck
I'm not sure if this is any help (probably not) but Tracpipe is being used quite a bit nowadays.
Here's a snippet from the Tracpipe website (Google "tracpipe" to read more)[FONT=Arial, Helvetica, sans-serif][SIZE=-1]
"TracPipe stainless steel semi-rigid gas pipe is quickly becoming the recognized alternative to traditional rigid copper or steel, installed between meter and appliance. (For installations before the meter it is possible to use TracPipe and reference should be made to BS EN 12007-1). "[/SIZE][/FONT]