DammDo a google image search for "bathroom zones", and 18 of the first 20 results show one!
It takes concerted effort to find a correct diagram unfortunately.
I looked through a few and finally picked a poor one!!
DammDo a google image search for "bathroom zones", and 18 of the first 20 results show one!
It takes concerted effort to find a correct diagram unfortunately.
The 60cm seems quite specific though, is that some general guidance for sinks instead of bathroom-specific zones?Do a google image search for "bathroom zones", and 18 of the first 20 results show one!
It takes concerted effort to find a correct diagram unfortunately.
There's nothing specific in BS7671. There are a few documents that mention 30cm, e.g. NHBC technical notes, GN1, and those fine fellows upholding the standards of the industry at NICEIC...The 60cm seems quite specific though, is that some general guidance for sinks instead of bathroom-specific zones?
The 60cm seems quite specific though, is that some general guidance for sinks instead of bathroom-specific zones?
What happened one site produced the drawing with the zone around the sink. A second site who wanted to put a pic on their site Googled it and up came the zoned sink drawing, they copied it. Can you see where this is going.
Thanks JulieWhen you have a bath or shower, the space around is defined by zones 0, 1 & 2, and there are different requirements for ingress protection (waterproofness), types of equipment etc for each zone.
There is also a regulation which prevents having a standard socket outlet within 3 metres.
However this only applies within the room itself, or if there isn't a barrier (door, window, hatch etc).
So you can have an outlet directly outside the bathroom door for example, but if you remove the door then it would be prohibited.
If the shower is contained within a proper enclosure (not just a leaky cubicle), again ok within 3 metres, (but not within zone 2), remove the shower enclosure then prohibited etc.
View attachment 93696
I manage to speak to him today ( he was booked by the lettings agent so not had any contact with him before ) . He said the reason for putting the isolator switch outside and making it waterproof ( even though it was outside zone 2 ) was that if someone was drunk and stepped out of the shower or reached around the bath and switched on the switch ( this is above the door so not easy to reach from either place except if you stepped out) then it would be a safety issue whereas if you went outside the bathroom you were more likely to be dressed .Just to add that the report says:
"Low voltage (e.g. 230 volt) socket-outlets sited at least 3 m from zone 1 (701.512.3) Fan isolation switch in bathroom and on-suite. x2 in total"
The first section was auto-completed from ticking a box elsewhere. I still think it actually refers to having fan isolators in zone 2. The "socket" could be a complete red herring, due to the wrong schedule item being chosen.
he mentioned that the lights are IP20 . So if they are outside zone 2 , they should still be ok ?When you have a bath or shower, the space around is defined by zones 0, 1 & 2, and there are different requirements for ingress protection (waterproofness), types of equipment etc for each zone.
There is also a regulation which prevents having a standard socket outlet within 3 metres.
However this only applies within the room itself, or if there isn't a barrier (door, window, hatch etc).
So you can have an outlet directly outside the bathroom door for example, but if you remove the door then it would be prohibited.
If the shower is contained within a proper enclosure (not just a leaky cubicle), again ok within 3 metres, (but not within zone 2), remove the shower enclosure then prohibited etc.
View attachment 93696
That is a ridiculous reason if they are not in zone 2 there is no issue.I manage to speak to him today ( he was booked by the lettings agent so not had any contact with him before ) . He said the reason for putting the isolator switch outside and making it waterproof ( even though it was outside zone 2 ) was that if someone was drunk and stepped out of the shower or reached around the bath and switched on the switch ( this is above the door so not easy to reach from either place except if you stepped out) then it would be a safety issue whereas if you went outside the bathroom you were more likely to be dressed .
Complain to Napit. Take some photo's, say you are willing to email them photos and the report, and quote this response.I manage to speak to him today ( he was booked by the lettings agent so not had any contact with him before ) . He said the reason for putting the isolator switch outside and making it waterproof ( even though it was outside zone 2 ) was that if someone was drunk and stepped out of the shower or reached around the bath and switched on the switch ( this is above the door so not easy to reach from either place except if you stepped out) then it would be a safety issue whereas if you went outside the bathroom you were more likely to be dressed .
Outside of Zone 2 i.e. just like anywhere else in the property IP2x is acceptable to the regs.he mentioned that the lights are IP20 . So if they are outside zone 2 , they should still be ok ?
thank you for the adviceOutside of Zone 2 i.e. just like anywhere else in the property IP2x is acceptable to the regs.
Would I fit them, depends, good modern ventilated bathroom, probably, old unventilated bathroom I would more than likely fit a higher rated fitting, however this would be by choice not compulsory.
sorry can I also ask...the socket under the kitchen sink he will not pass the report if it is not waterproof when I asked what regulation it is voilatiing as he said it is a safety hazard ..so i am a bit stuck there . I cant remember if there is a second switch but he mentioned 2 and changing them both. Since there are to plug in a dryer /washing machine ( there is no space in the kitchen for this and I am having the cracked plug in the garage replaced where the dryer and washing machine machine are plugged in , I was thinking of getting this taken out once I make sure it is not in use .Complain to Napit. Take some photo's, say you are willing to email them photos and the report, and quote this response.
You can't C2 something in case someone is drunk. It doesn't make sense anyway, by his logic you would need IP rated switches in the kitchen in case you washed up and then turned something on.
One of the flaws of the system is that the inspector has the final say.and can he refuse to give me a pass eicr just for this issue
ok thank you..that is really good adviceOne of the flaws of the system is that the inspector has the final say.
But the inspector is supposed to test according to the regs. There is also a document called Best Practise Guide 4 (free online).
The scheme he belongs to (the same scheme as I do) has rules. The scheme rules are that complaints must first be made in writing to the electrician concerned. If that doesn't get anywhere, then you can complain to Napit.
I would draft a letter of complaint, saying other electricians (including other Napit members) do not agree with the observations, and could they help get this matter resolved. See what happens.
yes he did the original EICR but I am getting another quote as well. Both have said parts are unavailable/expensive to source and best to replace . He is adamant on not issuing the pass certificate if I do not get this changed . He kept saying it is your house and you can do whatever you want but this has been listed as a C2There is nothing wrong with that socket. Please tell me this isn't the same electrician you are using to replace your consumer unit in the other thread.
ok thank you Brian...this is the first time I am renting a place so i guess there is a lot to learnBeing generous, this is just another case of an electrician testing to what he thinks the rules should be, not what they actually are.
Being not so generous, it could be viewed as a money generating exercise.
Condemning the socket under the sink (on IP grounds) is beyond ridiculous. It's even mounted on the structure of the house, rather than the cupboard carcase (for which there is a tenuous argument that it's not permitted.)
Regarding the bathroom lights, there is a regulation that requires equipment to be suitable for the environment into which it is installed, but unless there is evidence of considerable condensation in this bathroom, I wouldn't consider this remotely applicable.
If fitting new lights in a bathroom, I think most of us would fit IP rated ones, but they are not a requirement.
yes switch was not cracked before inspection but i will have it replaced for sureBack at #55 there was mention of a cracked socket for washing machine and dryer?
It’s likely to crack again with two high load appliances being used at the same time.
Just an observation.
Hang on..... so, the inspecting 'electrician' damaged the faceplate?!yes switch was not cracked before inspection but i will have it replaced for sure
yes it was not cracked before . My dryer was plugged into it before and I used it regularly and there was no crack .Hang on..... so, the inspecting 'electrician' damaged the faceplate?!
If a 2G socket has been provided for a washing machine and an adjacent tumble drier, then it should be replaced by a dual box and 2 x 1G sockets. (As it should have been on first installation)Back at #55 there was mention of a cracked socket for washing machine and dryer?
It’s likely to crack again with two high load appliances being used at the same time.
Just an observation.
More to the point, you need someone, like timhoward, to do the first EICR. Someone who knows what he's doing.My point is that you don't need the same person to do remedials, and you don't need another EICR, you just need someone to evaluate matters and do required remedials who takes a professional approach.
All the best with this.
I think you are being generous assuming it was actually a properly qualified electrician doing the EICRBeing generous, this is just another case of an electrician testing to what he thinks the rules should be, not what they actually are.
Being not so generous, it could be viewed as a money generating exercise.
Condemning the socket under the sink (on IP grounds) is beyond ridiculous. It's even mounted on the structure of the house, rather than the cupboard carcase (for which there is a tenuous argument that it's not permitted.)
Regarding the bathroom lights, there is a regulation that requires equipment to be suitable for the environment into which it is installed, but unless there is evidence of considerable condensation in this bathroom, I wouldn't consider this remotely applicable.
If fitting new lights in a bathroom, I think most of us would fit IP rated ones, but they are not a requirement.
I need to check whats plugged in ...couldIf a 2G socket has been provided for a washing machine and an adjacent tumble drier, then it should be replaced by a dual box and 2 x 1G sockets. (As it should have been on first installation)
Also does the person who does the remedial work charge to.issue the EICR certificate . Or do I go back to te original EICR engineer to.show him the work done report . The guy who.has quoted me.for remedial.work is also charging me for a EICR certificate . Not sure how this worksGoing back to the original report, I would be very interested to know how quickly the RCD trips when you press the test button.
The readings on the report say >500 (x1) and >410 (x5). Assuming these are milliseconds, I think that even without a testing machine you could discern if it trips in 'about half a second' or 'instantaneously'.
If it proves that the RCD is in fact ok, then as far as I can see we are now reduced to one incorrect breaker and a possible shower circuit issue.
General point -
When I (rarely) do remedial work for someone else's EICR, if I disagree with a C2 I justify why on my write up citing relevant regulations and photographic evidence why . You don't actually need a certificate that says "satisfactory", you need written proof that required remedial work has happened, and for me I just use a letter. Here's two excepts from a recent one I wrote:
View attachment 93954
and a bit later:
View attachment 93955
My point is that you don't need the same person to do remedials, and you don't need another EICR, you just need someone to evaluate matters and do required remedials who takes a professional approach.
All the best with this.
I slightly despair at the system sometimes....it's not obvious how it is supposed to work.Also does the person who does the remedial work charge to.issue the EICR certificate . Or do I go back to te original EICR engineer to.show him the work done report . The guy who.has quoted me.for remedial.work is also charging me for a EICR certificate . Not sure how this works
Hi TimI slightly despair at the system sometimes....it's not obvious how it is supposed to work.
The thing is, people like to end up with a certificate that says "Satisfactory". Like a car MOT. But the PRS law clearly says you just need written evidence that the remedial work has been done (I quoted the law in the letter I previously posted).
So you might reasonably be charged for some admin time to write a letter, but it isn't necessary to have another EICR report / certificate done. That said, if the fee is modest there is nothing wrong with having another set of EICR paperwork with no (or only C3) observations, and Satisfactory on the front.
Hope that helps.
Also just to add in the bathroom anything under the bath/shower basin is considered to be zone 1, however if a tool is required to access under the bath/shower then it doesn’t have any zone.sorry can I also ask...the socket under the kitchen sink he will not pass the report if it is not waterproof when I asked what regulation it is voilatiing as he said it is a safety hazard ..so i am a bit stuck there . I cant remember if there is a second switch but he mentioned 2 and changing them both. Since there are to plug in a dryer /washing machine ( there is no space in the kitchen for this and I am having the cracked plug in the garage replaced where the dryer and washing machine machine are plugged in , I was thinking of getting this taken out once I make sure it is not in use .
But if it is and if there is no regulation do i still have to change it ? and can he refuse to give me a pass eicr just for this issue . But if it really is a safety hazard I can look at changing ot taking this outView attachment 93928
Yes you can but please do not use the same electrician find someone reputable. Some of these apparent Code 2s a different electrician will say works are not required.Hi Tim
He will charge £120 to.issue a pass/ new EICR . Can i submit the oŕiginal EICR with the evidence or remedial work done . And who do I submit this to.please
Yes trying to get other quotes nowYes you can but please do not use the same electrician find someone reputable. Some of these apparent Code 2s a different electrician will say works are not required.
Unless anyone (like a letting agent) asks for it, you just have to hold it. A bit like no one comes knocking to see your car MOT.Can i submit the oŕiginal EICR with the evidence or remedial work done . And who do I submit this to.please
Hi Tim
He will charge £120 to.issue a pass/ new EICR . Can i submit the oŕiginal EICR with the evidence or remedial work done . And who do I submit this to.please