Pictures of the main incomer RCD unit.

Its huge

ImageUploadedByTapatalk1376345015.252399.jpgImageUploadedByTapatalk1376345061.265077.jpg
 
Brilliant, would be useful as a means of showing people who don't understand exactly what is going on inside the magic little box with a test button on it.
 
Surely the earth wire shouldn't be fed through the sensor should it? otherwise any leakage to earth would come back on the wire and cancel out. Am I right in thinking that the device trips the TP MCB by effectively overloading the phase with the small brown wired going through? or is the module to the right the part that causes it to disconnect
 
Doesn't look like the earth is going through the sense coil to me, victim only viewing on my phone .

It's the same setup as a residual current/leakage relay and shunt trip used with MCCBs to give the same protection.
You have a device on the side of the normal breaker which is interlocked with the tripping mechanism of the breaker and trips it that way.
 