Evening all

Try to rack my brain about whether this would work.....

Customer on a job wants to add a 3rd switch on a lighting circuit, however it is near impossible to get from the 2way switch but easy to get from the first switch

Will having the intermediate switch where the feed and switch wire work.....

Cheers

T
 
Yup,So instead of joining the 3rd cores together at the inter, feed in joined to go to common one of the 2 way switches, light feed joined to go off to common on the other 2 way, strappers as per usual on the inter.
 
Ha! Someone may explain it better or if you're lucky, draw a pretty picture!

So using your colours of choice:

L1 brown, l2 grey black common at the 2 ways

At the intermediate: brown and greys into L1 and L2 as normal.
Join one black to permanent live in
Join others black to switched live to light
 
Don't know if this helps. Orange is a switch.
Middle one is intermediate, either as shown, or crossed over.
1630704348323.png
 
I suppose the easiest way of thinking about it is to take the normal basic 2 way switch setup with 2 strappers between L1 to L1 and L2 to L2. Then the feed to the common on one switch, and the load from the common on the other switch.
All you are doing is extending each common to the middle using the 3rd core.

The intermediate switch is just swapping the two strappers over and could be at any point on the circuit, or not be there at all.
 
To sum up:
Either of the two normal configurations will work just fine.
@timhoward shows the 'conventional' option above.
@littlespark describes the 'conversion' option. In this case, where all three terminals of both 2-ways are connected together with L & SL paralleled to L1 and L2, it doesn't matter where in the run of strappers they tap in provided they are both on the same side of the intermediate switch.
 
Had to read this thread a few times, but I think I got it.

So my understanding is that these are the two options described above - please correct me if I am wrong (and forgive my crude PowerPoint drawings)

opt1.png


and

opt2.png
 
It's still wrong. PL and SL must tap into the brown and grey of the same strapper cable. Imagine they were paralelled at one of the 2-ways, and then just transferred to the other end of the same strapper cable.
 
Yes. I think manufacturers are inconsistent with labelleling L1 and L2 on intermediates. Traditionally I recall it being L1 for both 'brown' terminals and L2 for both 'grey', but have seen drawings as per yours with L1 for both terminals facing one 2-way and L2 for both facing the other. Perhaps someone could confirm? I don't usually install light switches so it's ages sinnce I looked at one.
 
Yes. I think manufacturers are inconsistent with labelleling L1 and L2 on intermediates. Traditionally I recall it being L1 for both 'brown' terminals and L2 for both 'grey', but have seen drawings as per yours with L1 for both terminals facing one 2-way and L2 for both facing the other. Perhaps someone could confirm? I don't usually install light switches so it's ages sinnce I looked at one.
You're right, they do vary from manufacturer
 
You're right, they do vary from manufacturer
They certainly do. More or less any combination you like ?
The common theme seems to be a terminal at the top gets connected to one or other at the bottom ?
(as you might imagine from the construction of the thing). Amongst others Schneider go for L1, L2, L3, L4
 

Attachments

  • 04EC4DED-4948-4B28-BC1B-F90CE56DD6B6.jpeg
    04EC4DED-4948-4B28-BC1B-F90CE56DD6B6.jpeg
    81.4 KB · Views: 75
  • 433B9BFF-7A33-4648-8D62-7759C7DAE8A7.jpeg
    433B9BFF-7A33-4648-8D62-7759C7DAE8A7.jpeg
    41.1 KB · Views: 62
  • 368F2568-BF8F-4F76-9957-7A14F970B487.jpeg
    368F2568-BF8F-4F76-9957-7A14F970B487.jpeg
    61.1 KB · Views: 73

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
United Kingdom
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Feed and switch wire at an intermediate...
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25
Unsolved
--

Advert

Thread statistics

Created
TJC1,
Last reply from
cliffed,
Replies
25
Views
17,292

Advert

Back
Top