Discuss Final Circuits - Ring or Radial? in the UK Electrical Forum area at ElectriciansForums.net
Well I have the fluke 321, specs say for Amps 0-400.00 it has a 3 digit display, just out of interest I put it around a tail and pulling 11A put it on the main E get a reading of 00.6 switch the kettle on goes up to 02.1 is this right ? or is the meter out of range ? how can it register 400A if I only have two digits a decimal point then one digit ?
TNCS PME supply
J
It can't measure mA. This is the spec from the fluke website:
Range: 0-400A Resolution 0.1A
Range 0-40A (Fluke 322 only) Resolution 0.01A
A spec for a mA meter will be something like a 3mA range with resolution of 0.01mA and 30mA with resolution of 0.01mA, etc.
Not sure what's going on with your readings there.
I generally prefer radials, but the rfc has its uses. For example, i am currently wiring a small work area for a company. The heavy duty kit has its own 3ph supply or runs on air. But they need sockets to plug in some lights and over a small bench area. I would normally have put the sockets on a radial, especially as the area is only the size of a single garage, however I cannot avoid running some cable in insulation, method 103. This reduces 2.5 to 17A. So I cannot put in a 20A radial, so instead I'm putting in a 20A rfc (I would have made it 25A but couldn't get a 25A RCBO without special ordering it).
In domestic and commercial the rfc also has the advantage of "reach". With it's substantially reduced volt drop compared to a radial and it's ability to share the load over two legs, an rfc can be installed in a largish area that might require several radials (IT considerations aside). Or it can be used to reach third floor bedrooms involving long initial runs.
Rfcs are also useful for high integrity earthing, as you don't need to install an extra g/y return cpc as you do with radials.
Don't forget that an rfc does not have to be 32A/2.5mm. Other ocpd/cable combinations are available!
Viva la rfc! (even though I prefer radials)
Thanks buddy I couldn't quite work out the zero-400 zero is just that isn't it ?
Steve
Reply to Final Circuits - Ring or Radial? in the UK Electrical Forum area at ElectriciansForums.net
  • Locked
5K
Hi all, For clarity, I'm not a qualified electrician, but have a reasonable amount of experience as I've done plenty of wiring (signed off by a...