I'd drop all the sockets and try and see which ones lead to the fuse board. And rewire from the board till to you can meet the earth coming the other way. If your just missing 1 return earth leg then this shouldn't be to hard.
Usually a bit of pulling on cables can establish where they go.
I love rewiring these flats 2 of you can have one buttoned in 6-7 hours.
If all else fails you'll have to go surface
Why drop the sockets. Do a Zs at each and see where the difference is the greatest and you should find the missing "link" there, or there abouts