One year ago, not 10!
Main leakage was neutral to earth, not live to earth.
And lots of fun finding extension leads with surge protection stuffed behind beds.
Now all clear for new CU - thanks @Wilko

Interesting update. When you say all clear what are your ir readings now?

Fyi surge protection devices, rcd's and appliances will all give low and false IR readings ...
 
Interesting update. When you say all clear what are your ir readings now?
Fyi surge protection devices, rcd's and appliances will all give low and false IR readings ...
Yes indeed, it did take a few searches to find them all.:confused:
The kitchen ring L+N to E at 250V was initially too low to read on my meter, but not a dead short. Deleting the damaged cable brought the 2 radials to about 200M. By conclusion the global IR at 500V was 40M Ohms.
 
In reality no, but members of the public are encouraged to use accredited tradesmen because it supposedly gives them more assurance about the quality of workmanship.
As a landlord I have to be able to show that I took reasonable care in having my home tested (and soon worked on) by someone competent to do the job.
And there lies the problem.
 
Hi All - @naylorpd was mad kind enough to let me in for a look at the problem.
On arrival, clamping the tails did reveal a standing leakage of 70mA so there was likely to be a problem to solve. It turns out a fried USB outlet and a kitchen RFC fault were the major contributors. Fixing these two has reduced the installation leakage to 10mA with all appliances and boiler running etc.
The installation is 1980 (ish) TNCS PME , controlled by the original Wylex board with push button 5,15 and 30A mcb. There was a new kitchen fitted 10 years ago and one of the wall units has a mounting point in the middle of the cable safe zone. And sure enough probing the bracket through the back of the cupboard showed connection to the ring. Due to domestic practicalities we decided to deal with Kev's Revenge by disconnecting the damaged section for now. The RFC is now 2 radials with 15A OCPB, until a more convenient time to dismantle the kitchen, dig out the cable and repair it.

That's top feedback mate ............ Shame the chap who did the EICR wasn't as diligent.
 

Reply to Find electrician to trace earth leakage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
695
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
845
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
800
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Morning, Customer has a intermittent trip which I am trying to locate. 4 circuits on rcd. Two rings , cooker and hob and one I cannot find...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock