hi all any help would be appreciated. Been asked to sort out a smoke alarm which is linked to the kitchen door but not to the fire alarm.

I have attached attached a photo of the plan he gave me which states linked to door not fire alarm circuit. He has a 24v over door magnetic holdback which he wants to use again. Anyone done this before and what's the best way to do it?

IMG_6206.JPG
 
Why would you link a smoke alarm to a door? And why not a heat in the kitchen?
 
I'm not sure it has a heat alarm but asked for a smoke which is not linked to fire alarm. I'm guessing that means a mains power aico smoke to release the door if it sound rather than setting the fire alarm off with false alarms. Not sure if that is correct if anyone has any ideas would be appreciated
 
sounds like that's what he wants. normally this idea is used with fire alarm control panels so when the alarm activates, a 24V relay de=energises the door magnet. can't see how it can work with domestic smokes such as aico.
 
sounds like that's what he wants. normally this idea is used with fire alarm control panels so when the alarm activates, a 24V relay de=energises the door magnet. can't see how it can work with domestic smokes such as aico.
Only thing I thought was to use a aico relay base so if smoke goes off will release the door magnet. Only thing I'm not sure on is shouldn't all the fire doors close off the fire alarm circuit and doing this wouldn't release the kitchen door with the rest of the doors on the fire alarm. Also the overdoor is 24v so guessing a separate psu just for the one door is required. Seems a lot of messing about for one door and one smoke alarm
 
Why would you have a smoke alarm in a kitchen, when there is a heat alarm in the same room?

Maybe ask the person who did the design?
 
Why would you have a smoke alarm in a kitchen, when there is a heat alarm in the same room?

Maybe ask the person who did the design?
He says in another care home he's got they put a smoke in the same as his plans shown. The only way I can see doing it would be via a separate psu and aico relay base.
 
All that's going to happen is the door is going to close all the time from false activation, that's why heat detectors are fitted in the first place.
 
I suspect the entrance hall is a protected route and the door release and smoke detector are in place to prevent smoke on this route. It is possible the kitchen door which would form protection to a compartment opening could be left wedged open which would allow spread of smoke to the hall if a fire went unnoticed and the heat detector failed to activate the system so the best option is to fit a door mag with smoke detector.
 
I suspect the entrance hall is a protected route and the door release and smoke detector are in place to prevent smoke on this route. It is possible the kitchen door which would form protection to a compartment opening could be left wedged open which would allow spread of smoke to the hall if a fire went unnoticed and the heat detector failed to activate the system so the best option is to fit a door mag with smoke detector.

So would you say using the aico with relay base then a separate psu for the kitchen door only is the best way to do it?
 
Sounds like the best option. You should also identify the smoke detector as being standalone and not connected to the main system.
 
and when the door is propped open with the kitchen fire extinguisher?
 
Last edited:
You need to ensure that the door closes when either the stand alone or main alarm goes off. The acoustic option may be easier than two trigger feeds for the contactor. I suppose it will depend on the sensitivity and volume of the main alarm.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Dorset

Thread Information

Title
Fire alarm
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
20

Thread Tags

Advert

Thread statistics

Created
Southspark85,
Last reply from
Devonchris,
Replies
20
Views
3,360

Advert

Back
Top