Hi, been servicing a fire alarm and in some areas the devices are sending 3 different zones into fire? The engineer I work with says this is a wiring fault somewhere, I was just wondering how this happens, it's a conventional c-tec 8 zone panel.

Thanks

Chris
 
Never come across this one before, Logically to activate 3 zones at once the + from all 3 zones must be shorted as they share a common - with all zones and sounder circuits. But can not see them all being shorted and would imagine a fault led on all 3 zones.
Can only suggest at this time to remove all cables from 2 of the effected zones, dont worry about end of line caps, they will just show faults on the zones. then test the 3rd zone and see if the other 2 zones go into fire condition. If they do then panel is at fault. Would suggest doing this test first to save a lot wasted time looking for wiring faults.
 
Never come across this one before, Logically to activate 3 zones at once the + from all 3 zones must be shorted as they share a common - with all zones and sounder circuits. But can not see them all being shorted and would imagine a fault led on all 3 zones.
Can only suggest at this time to remove all cables from 2 of the effected zones, dont worry about end of line caps, they will just show faults on the zones. then test the 3rd zone and see if the other 2 zones go into fire condition. If they do then panel is at fault. Would suggest doing this test first to save a lot wasted time looking for wiring faults.


good thinking. i would suspect a panel fault.
 
Thanks tazz, i think that is the best way forward to take out 2 of the zones and see if the panel still shows faults on the other 2 zones. the zones that are effected are 2 4 & 8 and there is no current faults on the panel so this really rules out wiring problems like u say above, the chances are slim to none. thanks for your advice tazz we are back there tomorrow and will update u on the outcome. thanks
 
Ok when you disconnect zones they will show fault, its fire activation where looking for, will be interesting to have your feed back on this problem
good luck Dave
 
id also try puttng your eols in the zones,a fault on the zone might mask the problem,tho as tazz says its def the panel..
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fire alarm
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
cristafar,
Last reply from
alarm man,
Replies
5
Views
1,720

Advert

Back
Top