C

cristafar

Hi, been servicing a fire alarm and in some areas the devices are sending 3 different zones into fire? The engineer I work with says this is a wiring fault somewhere, I was just wondering how this happens, it's a conventional c-tec 8 zone panel.

Thanks

Chris
 
Never come across this one before, Logically to activate 3 zones at once the + from all 3 zones must be shorted as they share a common - with all zones and sounder circuits. But can not see them all being shorted and would imagine a fault led on all 3 zones.
Can only suggest at this time to remove all cables from 2 of the effected zones, dont worry about end of line caps, they will just show faults on the zones. then test the 3rd zone and see if the other 2 zones go into fire condition. If they do then panel is at fault. Would suggest doing this test first to save a lot wasted time looking for wiring faults.
 
Never come across this one before, Logically to activate 3 zones at once the + from all 3 zones must be shorted as they share a common - with all zones and sounder circuits. But can not see them all being shorted and would imagine a fault led on all 3 zones.
Can only suggest at this time to remove all cables from 2 of the effected zones, dont worry about end of line caps, they will just show faults on the zones. then test the 3rd zone and see if the other 2 zones go into fire condition. If they do then panel is at fault. Would suggest doing this test first to save a lot wasted time looking for wiring faults.


good thinking. i would suspect a panel fault.
 
Thanks tazz, i think that is the best way forward to take out 2 of the zones and see if the panel still shows faults on the other 2 zones. the zones that are effected are 2 4 & 8 and there is no current faults on the panel so this really rules out wiring problems like u say above, the chances are slim to none. thanks for your advice tazz we are back there tomorrow and will update u on the outcome. thanks
 
Ok when you disconnect zones they will show fault, its fire activation where looking for, will be interesting to have your feed back on this problem
good luck Dave
 

Reply to Fire alarm in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hi all, i'm just after a definitive answer regarding a fire alarm system in a communal area/stairwell. There are call points, smoke heads &...
Replies
4
Views
640
Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
Replies
38
Views
4K
I'm about to order this wired smoke alarm system as it can network but I just went to see how my existing fire alarms are hooked up and there...
Replies
12
Views
1K
Hi All, Please may I ask if light fixtures must now always be fitted by an electrician? also for domestic homes, is it okay for there to be a...
Replies
4
Views
817
I'm about to start first fixing this fire alarm in the industrial unit we are wiring, at the moment its totally empty and eventually will have a...
Replies
5
Views
892

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top