Hi all,

After some thoughts on the following scenario.

Block of 16 flats configured 4per floor over 4floors - on each floor is an electrical cupboard containing the DNO fuse, electric meter, switch fuse in metal housing.

The cupboards are in the communal staircase

Walls, floor and ceiling of cupboards are concrete - doors are currently standard construction albeit with suited locks

At my latest Elecsa visit my assessor pointed out that he felt the doors should be fire rated with intumescent seals, last week we had an FRA done on the building and it was again the opinion that the cupboard doors should be fire rated.

I am obviously aware of the requirment for the switch fuses to be of non combustible construction and we are fine on this, where I am being picked up is that the meter is plastic.

I sort of understand this position except for the fact that on a very similar job recently the DNO came in and fitted a double pole isolator in a plastic housing between the service head and the meter and told me the requirement for a non combustible housing doesn’t apply to kit they install.

So after a long winded intro what do people think? Would you fit fire rated doors or not?

Thanks

Paul
 
This has been picked up on the FRA but yes they should have protected doors to prevent spread onto the stairwell. It is irrelevant the type of equipment installed, those cupboards should not be on stairwells although if it is historic you are stuck with it. This is however not an electrical issue.
 
Yes and any cable/conduit or trunking entry holes should brseales as well
 
Block of 16 flats configured 4per floor over 4floors - on each floor is an electrical cupboard containing the DNO fuse, electric meter, switch fuse in metal housing.

The cupboards are in the communal staircase

Walls, floor and ceiling of cupboards are concrete - doors are currently standard construction albeit with suited locks

At my latest Elecsa visit my assessor pointed out that he felt the doors should be fire rated with intumescent seals, last week we had an FRA done on the building and it was again the opinion that the cupboard doors should be fire rated.

I am obviously aware of the requirment for the switch fuses to be of non combustible construction and we are fine on this, where I am being picked up is that the meter is plastic.

The selection of doors is not your responsibility

The meter is outside your remit.

I would recommend you ask Elecsa to confirm, in writing, what precisely the issues are, and more importantly which regs are being broken.

I would suggest that your assessor is clutching at straws
 
The selection of doors is not your responsibility

The meter is outside your remit.

I would recommend you ask Elecsa to confirm, in writing, what precisely the issues are, and more importantly which regs are being broken.

I would suggest that your assessor is clutching at straws
Might not be the OPs responsibility Murdoch, but common sense will dictate that the cupboard doors should be fire retarded, don't want a Mini Grenfell on our hands do we?
 
Might not be the OPs responsibility Murdoch, but common sense will dictate that the cupboard doors should be fire retarded, don't want a Mini Grenfell on our hands do we?

As I said its not OUR responsibility to specify doors ................

As for Grenfell - we just need the DCLG to accept they write very poorly written building regs that are too open to interpretation.
 
As I said its not OUR responsibility to specify doors ................

As for Grenfell - we just need the DCLG to accept they write very poorly written building regs that are too open to interpretation.
Yeah OK point taken Mate.
 
The FRA will dictate at what level, if any the fire doors need to be rated at. This is outside if the scope of BS7671.

Also BS7671 only covers the consumers side of the installation so the DNO meter is not under that remit. Even if it was a check meter you would you consider a meter to be ‘similer switchgear’?
 
The FRA will dictate at what level, if any the fire doors need to be rated at. This is outside if the scope of BS7671.

Also BS7671 only covers the consumers side of the installation so the DNO meter is not under that remit. Even if it was a check meter you would you consider a meter to be ‘similer switchgear’?
Similar I'm in my School teacher mode this morning, marking bad spelling, no offence meant.
 
I should have said I am responsible for the complete refurb of the building inside and out.

Building is 1960’s in origin and location of equipment is fixed and no scope to change - all we have done to date is fit new locks to the existing doors and have them decorated.

When we had building control look at the place at the outset of the project the doors didn’t come up as an issue - only now once we have almost finished are they coming up as an issue.

Thanks for everyones input I will wait for the full FRA report and talk to the client on how best we do something to comply - I see a trip to Cotswold intumescents or some new doors in my future.

Paul
 
Unless you are well versed with the protection of openings to protected walls and stairwells I would advise professional help as it is not just a case of fitting some strips to the doors.
 
Wonder why the Elecsa assessor is poking his nose in things that are clearly outside our remit?

Maybe next year, distract him with nicer biscuits...........
 
I expect he/she has been on a short course and is trying to be clever. This appears to be a major oversight by building control as fire safety/control is top of the list.
 
The building control discussion was held in 2016 and the argument used by them and the client at the time was pre-existing circumstances, obviously this was well before Grenfell.

I have building control and a specialist fire engineering firm in next week to cover fire sealing of other areas of the building so will see what they recommend.
 

Reply to Fire rating communal Electrical cupboards in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
422
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted...
Replies
20
Views
2K
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
4K
Anyone got a solid answer on what the legal responsibilities are of building management companies when it comes to certifying their part of an...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock