I understand that when cables penetrate a fire-rated wall entering in to a consumer unit, appropriate fire-stopping measures are required to maintain the wall’s fire resistance. However, in scenarios where the consumer unit is mounted with a clearance from the wall, such that the wall’s fire-rated properties remain uncompromised, is it still a regulatory requirement to seal the rear cable entries of the consumer unit with fire-rated materials? Additionally, if sealing is required, what fire-rated materials or methods are typically recommended for this application? Clarification on both points would be greatly appreciated.
 
My understanding is it's not necessary unless compromising a fire barrier. Hager instructions:

Cable Access:
Cable access into the metal consumer unit must maintain the integrity of the non-combustable consumer unit so far as reasonably practicable. This can generally be achieved by the installer ensuring that cable access holes they make in the enclosure do not to leave gaps greater than:
· 1.0 mm for the horizontal top surface and
· 2.5 mm for all other surfaces of the enclosure that are accessible after installation.
For rear cable access, the minimum number of knockout(s) shall be removed. Tests on hager consumer units have indicated that there is no specific need for external fire rated cable glands or intumescent sealing in addition to the guidance below, with respect to achieving a non-combustible enclosure. However this does not preclude the designer/installer from using fire rated cable glands or external intumescent sealing should they consider necessary. Internal intumescent pads shall not be used.

 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

LmarshallSparks

Supporter
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician
Business Name
Marshall’s Co.

Thread Information

Title
Fire Rating - Rear Knockouts @ Consumer Unit
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
LmarshallSparks,
Last reply from
Pretty Mouth,
Replies
1
Views
248

Advert

Back
Top