Discuss First time doing an EICR on a flat in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
0
Hi all
Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block.
Carried out a ZE test got 14 ohms and got same reading when did ZS on the board (yes did disconnect earth for ZE) .. the main earth is wired into the service block .. I’m guessing the orange cable is going to a main fuse in the plant room and is armoured ..IMG_4801.png
 
TL;DR
Should the ze be done from the earth block rather than the main from the service head ??
I.e connect earth from MFT to block them probe onto terminals inside the DB ??
Last edited by a moderator:
The orange cable will go to the main incomer into a Ryfield or similar fused board.
The cable is split concentric, (Google it if you're not familiar) not SWA /Armoured.
Thanks for your reply have done mostly commercial and houses .. was baffled why the ze and as we’re same value .. would I be picking up parallel earths on this setup ?
 
It looks like the main earth into the consumer unit is connected to the service head.
If the Ze is that high it feels like there is no Neutral - Earth link in that head.
Did you try a Ze to that MET?
 
It looks like the main earth into the consumer unit is connected to the service head.
If the Ze is that high it feels like there is no Neutral - Earth link in that head.
Did you try a Ze to that MET?
No I didn’t i am going back to replace the cooker switch this week and will try and see what the reading is .. thanks in advance
 
Could be MICC, could be a concentric cable probably split concentric and the bare earth cores are just wrapped in tape. Orange split concentric often denote SNE systems.
 
If it was MICC , there would (should) be a proper pot on the end.
I’m going with split concentric.

Depending on age of the building, the water pipes could be metal, bonded to the MET, and also bonded at the main incomer, and in every other flat
 

Reply to First time doing an EICR on a flat in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
927
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
339
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
561

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock