Discuss First time doing an EICR on a flat in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all
Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block.
Carried out a ZE test got 14 ohms and got same reading when did ZS on the board (yes did disconnect earth for ZE) .. the main earth is wired into the service block .. I’m guessing the orange cable is going to a main fuse in the plant room and is armoured ..IMG_4801.png
TL;DR
Should the ze be done from the earth block rather than the main from the service head ??
I.e connect earth from MFT to block them probe onto terminals inside the DB ??
The orange cable will go to the main incomer into a Ryfield or similar fused board.
The cable is split concentric, (Google it if you're not familiar) not SWA /Armoured.
Thanks for your reply have done mostly commercial and houses .. was baffled why the ze and as we’re same value .. would I be picking up parallel earths on this setup ?
It looks like the main earth into the consumer unit is connected to the service head.
If the Ze is that high it feels like there is no Neutral - Earth link in that head.
Did you try a Ze to that MET?
No I didn’t i am going back to replace the cooker switch this week and will try and see what the reading is .. thanks in advance
Could be MICC, could be a concentric cable probably split concentric and the bare earth cores are just wrapped in tape. Orange split concentric often denote SNE systems.
If it was MICC , there would (should) be a proper pot on the end.
I’m going with split concentric.
Depending on age of the building, the water pipes could be metal, bonded to the MET, and also bonded at the main incomer, and in every other flat
Reply to First time doing an EICR on a flat in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...